I'm looking to buy some cable for my solar installation and happened to find a 2m length of black BS 6195 Type 4 cable (1993) left over from another job. I never throw anything like that away and try to use stuff that's left over if I can rather than just buying more.

 

The distance from my controller to batteries is about 6ft, so would this cable suitable be as one of the connections and just buy an equivalent length of 25mm2 battery cable in red? The only thing is that the multi-strands of the black cable don't look like they're copper?

Edited by blackrose
Link to comment
Share on other sites

11 minutes ago, jonathanA said:

I'd have thought 25mm might be a bit large for the terminals on your controller ? 

 

If not happy days...

 

It might be I'm not sure. I've bought the Epever 60amp mppt. I'll give it a go.

10 minutes ago, ditchcrawler said:

Don't forget the fuse at the battery end

 

Yes will do.. I need to understand the fuse rating I need. Just in the positive side?

 

Link to comment
Share on other sites

13 minutes ago, blackrose said:

 

It might be I'm not sure. I've bought the Epever 60amp mppt. I'll give it a go.

 

Yes will do.. I need to understand the fuse rating I need. Just in the positive side?

 

60A controller would have thought 60A fuse.  And yes in +ve.

Edited by jonathanA
Link to comment
Share on other sites

24 minutes ago, blackrose said:

Ok thanks David. So I only need 4mm2 cable? It seems very thin but easier and cheaper to install I suppose.

 

 

6 minutes ago, Jen-in-Wellies said:

That's the advantage of series wiring and high voltage for transmission. Much thinner wire needed for the same power going through.

 

 

Thats why on 'mains' voltage you can have a 25 metre (50 mt return length) extension lead that is only 1.5mm2.

 

(I get even less losses on my 120v panel using 6mm2 which fits nicely into the MC4 connectors)

Link to comment
Share on other sites

32 minutes ago, Loddon said:

It's worth thinking about what size the cable would need to be for the lower voltage parallel operation. Then size your cables to whichever is the greater just in case.

 

 

Yes I was thinking that too, then there's no retrofitting.

 

I'm still a bit unclear on parallel or series panel connection. You and Alan de Enfield recommended parallel but everyone else including Bimble are saying series. I've looked at the advantages and disadvantages of both online but the website I looked at was written from the perspective of someone who recommend series.

 

https://www.explorist.life/solar-panels-series-vs-parallel/

Link to comment
Share on other sites

You only have two panels. If you place them close together and remember not to moor in shade, then there are no advantages to parallel. Perhaps easier for you to arrange, with a wide beam. Depends on the roof width and panel sizes. More of a problem when there are a lot of panels strung out along the length of a narrowboat roof and one getting shaded is more likely. Then the series advantage of fewer joints and fuses and thinner cable makes total sense.

Jen

Link to comment
Share on other sites

1 hour ago, blackrose said:

 

Yes I was thinking that too, then there's no retrofitting.

 

I'm still a bit unclear on parallel or series panel connection. You and Alan de Enfield recommended parallel but everyone else including Bimble are saying series. I've looked at the advantages and disadvantages of both online but the website I looked at was written from the perspective of someone who recommend series.

 

https://www.explorist.life/solar-panels-series-vs-parallel/

Series is good if you have "low voltage" panels i.e. about 20v then you need to be concerned about volt drop and shading. With 43v panels parallel is fine less concern about volt drop and less concern about shading 

Link to comment
Share on other sites

2 hours ago, Jen-in-Wellies said:

That's the advantage of series wiring and high voltage for transmission. Much thinner wire needed for the same power going through.

 

Indeed, it is why the National Grid operates between 400,000 and 275,000 volts and distribution to the local substation down to 11,000 volts.

 

The cable cross sectional area would be massive if all electricity was distributed at 230 volts.

 

Link to comment
Share on other sites

1 hour ago, Loddon said:

Series is good if you have "low voltage" panels i.e. about 20v then you need to be concerned about volt drop and shading. With 43v panels parallel is fine less concern about volt drop and less concern about shading 

 

My panels are 120v EACH, if I wired them in series I'd soon be up in 'dangerous DC voltage' country. 120v is bad enough.

Link to comment
Share on other sites

3 hours ago, Jen-in-Wellies said:

You only have two panels. If you place them close together and remember not to moor in shade, then there are no advantages to parallel. Perhaps easier for you to arrange, with a wide beam. 

 

I'm going to have 2 x 2m long panels arranged end to end down the centre of the roof. They're just over a metre wide which gives me enough room to walk down either side. 

 

So that's 4m length of panels to be kept out of the shade. To be honest during that recent heatwave I went out onto the river to search for shade and it wasn't easy to find. If I wire the panels in series I assume the combined voltage isn't a safety issue?

https://www.bimblesolar.com/455w-canadian-solar-panel

 

Parallel installation would require 16mm2 cables and it looks like a more complex installation so I think I'll connect in series.

 

I'm sure I can do a decent installation once I know exactly what I'm doing, but my technical electrical knowledge is crap so I'm having to check and recheck everything. 

Edited by blackrose
Link to comment
Share on other sites

25 minutes ago, blackrose said:

If I wire the panels in series I assume the combined voltage isn't a safety issue?

Anything over 48V is potentially a safety issue. Cover the panels with blankets when working on the wiring and ensure there isn't exposed circuitry where inquisitive fingers can get to when finished. Ensure that any fuses, holders, etc that are used on the solar side are rated for the voltage. MC4 connectors are good in this respect. Even when disconnected the live terminals are recessed.

Jen

Edited by Jen-in-Wellies
  • Greenie 2
Link to comment
Share on other sites

2 minutes ago, blackrose said:

Why do the panels have to be covered when you're working on the system? Why can't they just be disconnected/isolated? Does the voltage have to go somewhere if they're left uncovered?

If they are producing power then its not good to disconnect under load as it causes arcing and connectors are  not rated for disconnect current, covering them prevents this.

View it as turning off the switch on the wall

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.