woke up this morning, to 2 red lights on my galvanic isolator status monitor.

Will did out paperwork to see what this means.

But had this fitted since early 2012, and first time this has had any of the 2 LEDs, let alone both together.

Oh well I imagine this is going to cost me one way or another.

 

Happy days

 

Col

Link to comment
Share on other sites

Thankyou for the replies.

 

I've checked the shore lead plug and socket, I've also used another shore power lead same thing, both LEDs still lit.

I am now going to carry out your suggestions, and disconnect all appliances and see what happens

 

Ta

 

Col

Link to comment
Share on other sites

Tried the above, the 2 Leds flicking alternately, then both on for 15 seconds then back to flicking,or both off.

 

Rang up Vic at Safeshore Marine Galvanic isolators and been advised that the above will possibly new boat, or someone's plugged in,or welding, new on the yard.

Give it a few days, or have a word with neighbours.Excellent service and advice from Safeshore marine,

 

If problem persists to get in contact and he will advise further,but what ever has changed outside, may sort it self out.

And yes we do have welding being carried out, but his bigger than me.

 

It's one of those types of equipment if you don't see it doing nothing, it's working!!

Now it's flashing it proves somethings wrong,it works, See Pyscloud, David, kris

 

Col

Edited by bigcol
Link to comment
Share on other sites

Tried the above, the 2 Leds flicking alternately, then both on for 15 seconds then back to flicking,or both off.

 

Rang up Vic at Safeshore Marine Galvanic isolators and been advised that the above will possibly new boat, or someone's plugged in,or welding, new on the yard.

Give it a few days, or have a word with neighbours.Excellent service and advice from Safeshore marine,

 

If problem persists to get in contact and he will advise further,but what ever has changed outside, may sort it self out.

And yes we do have welding being carried out, but his bigger than me.

 

It's one of those types of equipment if you don't see it doing nothing, it's working!!

Now it's flashing it proves somethings wrong,it works, See Pyscloud, David, kris

 

Col

but is it protecting your boat or letting the volts flow through your hull?

Link to comment
Share on other sites

That's a good question? your right!, if the LEDs are lit, then this means that the boat isn't being protected now??

Sometimes there off, sometimes flickering between the two.

 

So as per your post,the unit showing me there's a exterior fault, but am I still protected,?

 

 

Col

 

Ps Blizzard, yep Now sitting here, while slowly the boat is disintegrating, by the eels, lol

Edited by bigcol
Link to comment
Share on other sites

That's a good question? your right!, if the LEDs are lit, then this means that the boat isn't being protected now??

Sometimes there off, sometimes flickering between the two.

 

So as per your post,the unit showing me there's a exterior fault, but am I still protected,?

 

 

Col

 

Ps Blizzard, yep Now sitting here, while slowly the boat is disintegrating, by the eels, lol

Possibly not, there must be some current flow to light the led's. The source of the earth leakage needs to be found. Could it be possible for any water to have got into your AC system on your boat?

Link to comment
Share on other sites

Did Vic take you though the procedure to test your GI? You can do it with a new 9v battery or with a multimeter (shore power disconnected). If both leds are lit the diodes are in conduction, but don't panic, it just means that you effectively have no GI. Your boat's not going to corrode away in a few days.

Edited by blackrose
Link to comment
Share on other sites

 

hi flyboy

 

Yes we did check plugs sockets, took apart, tried different landline leads,

etc everything seems Good on the boat.

 

I don't know when land line disconnected, but just put genny on, no LEDs

But don't know if it works that way(different circuit)

 

The AC system is dry,

Still thinking

But lights are now staying off, longer than staying on.

Welding and grinding is happening in the yard, so time will tell.

 

Thanks

 

Col

Link to comment
Share on other sites

One LED lit indicates a problem with AC, if the second is lot means a problem with DC, both LEDs on is definitely a "oh tilt" moment.

Hope you soon sort it out.

Phil

 

Normally the two LED's are used to indicate each of the back to back pairs of diodes that form the main part of the isolator are conducting and not blocking. Either one on indicates a DC current flow in one of each direction. Both on continuously indicates a significant AC leakage and that the GI might as well not be there.

 

It doesn't mean that its not working as intended though, just that external currents are forcing it into conduction.

 

Schematic of typical GI to better explain above.

 

galvanicisolatorwithcapacitorschema.jpg

Each diode forward biased requires 0.6 volt to conduct, so having two in series puts a 1.2 volt block on stray currents in each direction. The capacitor is a safety feature to allow conduction of AC in fault situation, obligatory for ABYC compliance.

Edited by by'eck
Link to comment
Share on other sites

Did Vic take you though the procedure to test your GI? You can do it with a new 9v battery or with a multimeter (shore power disconnected). If both leds are lit the diodes are in conduction, but don't panic, it just means that you effectively have no GI. Your boat's not going to corrode away in a few days.

Hi Blackrose.

yes done the batt test, it seems as VIC said that someone in the yard has a problem.

He said the LEDs are hyper sensitive, so the flashing and coming on, is down to someone else's earth problem.

 

Have to say, Vic Safesure. Was excellent spending time going through test and problem with me.

 

Col

Link to comment
Share on other sites

Several years ago I discovered that the leds of my safeshore status monitor were lit and the diodes had probably been conducting for quite a long time (hence no protection),because I hadn't realised the status monitor leads had become disconnected.

 

An electrician friend of mine reckoned that the house (on an island on the Thames) where I was taking my shore power from, wasn't properly earthed and was using my boat as its earth path!

 

I was alarmed by this and I only got the boat out of the water last summer, but there was no pitting or corrosion.

 

Have to say, Vic Safesure. Was excellent spending time going through test and problem with me.

 

Yes, I've spoken to him several times and he is good. He always has time to go through everything and is never in a rush.

Edited by blackrose
Link to comment
Share on other sites

Just to confirm as previous post

 

(LEDs haven't come on for the last hour or so.)

And have remained off as of now.

So all back to right!

 

someone visiting yard with dodgy tool, or dodgy appliance on their boat

Thankyou all. For your advice, all sorted

 

 

 

Col

Edited by bigcol
Link to comment
Share on other sites

Maybe it's like at my mooring (about a mile away) where the shared earth return is quite high impedance. We found that 1 of the 4 boats had some equipment that was leaky but not quite by enough to trip the rcd. This leakage current preferred to go back to the substation via the other boats' earth connections instead of via the designated supply cable.

Link to comment
Share on other sites

  • 2 weeks later...

Ive just tested my Safeshore GI with 2 different digital multimeters and it's continually reading 1 (as per Diode Test function on meter) with shoreline disconnected. Damn things shot I suspect, but is a good 8 years old, so probably time for a new one.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.