Webasto header tank height


Featured Posts

I'm juggling the options on my Webasto install.   Specifically, the location of the header tank.  

 

The Webasto unit will be in the engine compartment - as is the calorifier, which is the first heat demand, then through the bulkhead and onto the radiator ring. 

 

How much height difference is required for the header over the rest of the system (boiler, calorifier, rads, pipework)?  

 

If it is just "higher than" - then I would hope that I can keep it all in the engine compartment - achieving a bit of height difference while also still being able to fill/top it up. 

 

But if it needs a significant height difference, then i would have to take the header into the main cabin - into what will be the bathroom - and locate it on the rear bulkhead wall and run the pipes down and back out into the engine bay.   this is a faff as it takes up wall space in the bathroom and will require boxing into a cupboard etc, and means more pipe holes in the steel bulkhead. 

 

in time honoured fashion, a splendid options diagram included below:

 

Any thoughts?  

 

Option 1:

 

image.png.7abe17309fad394b53ac8b312438ba86.png

 

 

 

 

Option 2: 

 

image.png.1258cbb98719b1e319ace717cbcd9f75.png

 

 

 

 

 

Edited by TandC
Link to comment
Share on other sites

Higher than the highest point on the system is fine.  Take one pipe only from the bottom of the tank onto the circuit at the high point, no over the top pipe required. It will vent and allow for expansion. Volume needs to be 5% of the total water volume or more.

Link to comment
Share on other sites

13 minutes ago, Tracy D'arth said:

Take one pipe only from the bottom of the tank onto the circuit at the high point, no over the top pipe required.

That pipe should also rise continuously from the high point or the radiator/calorifier circuit to the header tank. Not so easy if the high point is a radiator at the front of the cabin.

Link to comment
Share on other sites

18 minutes ago, Tonka said:

Are you putting the calorifier and the rads on the same circuit ? When you say engine compartment are we saying under floor in a cruiser stern

Yes - cruiser stern 10ft wide.  The webasto will be on the right side just above the uxter plate, and the calorifier will be sat on the baseplate up against the bulkhead, to the right of engine.    22mm pipes to 15mm feeds to first the calorifier then on to a ring of 1 towel rail then 4 radiators in "there-and-back" single line going along the right side across the bow back down the left side.

 

 

This is the installation diagram from Webasto - describing this two-pipe/bypass valve arrangement with the header tanks as "the most efficient non-pressurised system"

 

I haven't really got my head into thinking much further at this stage - I was just trying to work out the issue of the header tank location first before I go try and plan some more. 

 

No doubt I shall be back for more shortly....

 

 

 

image.png

The pipe work is going to require to come from Webasto horizontal at the height of the Uxter plate through the bulkhead, and then drop down to within the boxing just above floor level - so two right angles effectively - before running off and then back in 22mm.  There will then be 15mm tee feeds to calorifier, towel rail, then the sequence of 4 rads. 

 

 

 

 

image.png.64ce69f425d9e7d7d7ee6f811ddc0ee0.png

 

 

 

And looking like this ish

 

 

 

image.png.8a88c0e0e1aa9126550b13b93febcac6.png

 

 

Link to comment
Share on other sites

The bypass valve/ tap does indeed give you the best system, and makes it far easier to bleed all the air as well.

This system used an existing loop from an old Alde boiler and we just inserted the 22mm from the Webasto to the first and last radiators. So long as the bottom of the tank is above every other bit of the system, the engine bay install will be OK.

20230731_170714.jpg

Link to comment
Share on other sites

40 minutes ago, matty40s said:

The bypass valve/ tap does indeed give you the best system, and makes it far easier to bleed all the air as well.

This system used an existing loop from an old Alde boiler and we just inserted the 22mm from the Webasto to the first and last radiators. So long as the bottom of the tank is above every other bit of the system, the engine bay install will be OK.

20230731_170714.jpg

How does the bypass valve, which needs to be open when the system is working, aid bleeding air?

Link to comment
Share on other sites

12 minutes ago, Tracy D'arth said:

How does the bypass valve, which needs to be open when the system is working, aid bleeding air?

With the bypass valve closed, all the return flow has to go through the header tank easily releasing any air.  It's not often you don't know all the answers 🙂!

  • Happy 1
Link to comment
Share on other sites

5 hours ago, TandC said:

Yes - cruiser stern 10ft wide.  The webasto will be on the right side just above the uxter plate, and the calorifier will be sat on the baseplate up against the bulkhead, to the right of engine.    22mm pipes to 15mm feeds to first the calorifier then on to a ring of 1 towel rail then 4 radiators in "there-and-back" single line going along the right side across the bow back down the left side.

 

 

This is the installation diagram from Webasto - describing this two-pipe/bypass valve arrangement with the header tanks as "the most efficient non-pressurised system"

 

I haven't really got my head into thinking much further at this stage - I was just trying to work out the issue of the header tank location first before I go try and plan some more. 

 

No doubt I shall be back for more shortly....

 

 

 

image.png

The pipe work is going to require to come from Webasto horizontal at the height of the Uxter plate through the bulkhead, and then drop down to within the boxing just above floor level - so two right angles effectively - before running off and then back in 22mm.  There will then be 15mm tee feeds to calorifier, towel rail, then the sequence of 4 rads. 

 

 

 

 

image.png.64ce69f425d9e7d7d7ee6f811ddc0ee0.png

 

 

 

And looking like this ish

 

 

 

image.png.8a88c0e0e1aa9126550b13b93febcac6.png

 

 

You'd probably get better circulation with the port and starboard side radiators on separate loops. Just tee off the port side loop within the engine room and run the transverse pipes on the engine side of the rear bulkhead. Less pipework overall and less resistance to the pumped flow.

Link to comment
Share on other sites

1 hour ago, Chris G said:

With the bypass valve closed, all the return flow has to go through the header tank easily releasing any air.  It's not often you don't know all the answers 🙂!

I don't see what difference 2 connections to the same pipe 6" apart make when one would do. And the valve is totally unnecessary. Forcing the circulation into a partially filled tank and out again will simply cause turbulence and possibly air entrainment into the water.

I reckon its bunkum.

Link to comment
Share on other sites

7 minutes ago, Tracy D'arth said:

I don't see what difference 2 connections to the same pipe 6" apart make when one would do. And the valve is totally unnecessary. Forcing the circulation into a partially filled tank and out again will simply cause turbulence and possibly air entrainment into the water.

I reckon its bunkum.

Perhaps RTFM.🙂

  • Greenie 1
Link to comment
Share on other sites

Good stuff.

 

 

On splitting into two separate loops - one serving the two rads on the port, one serving the three on the starboard...  I've had conflicting advice, with some saying it'd be more efficient run as I propose - one continuous loop.    It is easier to not have to take a second loop across from the starboard to the port side for various reasons of other electrics etc in the way.   So unless there is a really glaring reason, i think i will stick to the single loop.   It's marginal whether there is any more pipe involved and the boat is only 45ft long anyway. 

 

On the bypass valve - the Webasto manual and the folk at ButletTecknic recommend the two pipes/bypass valve to do what ChrisG says - micro air bubbles better expunged apparently.  

 

Well it's all a while off yet but the thinking bit is the bit that takes the longest...

 

Link to comment
Share on other sites

I just use a 30% solution of antifreeze. 50% may be too strong for some reason which I can't remember. The antifreeze has corrosion inhibitors which last anywhere from 2 to 5 years (standard blue or red longlife) essential in central heating systems to stop your rads corroding from the inside, but instead of draining down the system and refilling every few years you can drain some out and add a small amount of Morris Ankorsol to the bucket before refilling. I think the dose is about 3% of the entire systems volume so you need to do a rough calculation or write down how much fluid you originally put in.

Edited by blackrose
  • Greenie 1
Link to comment
Share on other sites

22 hours ago, blackrose said:

I just use a 30% solution of antifreeze. 50% may be too strong for some reason which I can't remember. The antifreeze has corrosion inhibitors which last anywhere from 2 to 5 years (standard blue or red longlife) essential in central heating systems to stop your rads corroding from the inside, but instead of draining down the system and refilling every few years you can drain some out and add a small amount of Morris Ankorsol to the bucket before refilling.

Just normal Car Antifreeze would be OK then?

I will more than likely drain her down completely as i did have a small leak, so will make good all joints. 

Once it is renewed, i will know its history, if that makes sense.

Edited by Floaty Me Boaty
Link to comment
Share on other sites

2 hours ago, blackrose said:

just use a 30% solution of antifreeze. 50% may be too strong for some reason which I can't remember.

 

It is to do with the specific heat capacity of antifreeze, which is lower than that of water. The higher the antifreeze concentration, the less heat the liquid can carry to the radiators. Note; Heat and temperature are two different things, that many seem to think are the same.

  • Greenie 1
Link to comment
Share on other sites

On 31/07/2023 at 21:38, TandC said:

Good stuff.

 

 

On splitting into two separate loops - one serving the two rads on the port, one serving the three on the starboard...  I've had conflicting advice, with some saying it'd be more efficient run as I propose - one continuous loop.    It is easier to not have to take a second loop across from the starboard to the port side for various reasons of other electrics etc in the way.   So unless there is a really glaring reason, i think i will stick to the single loop.   It's marginal whether there is any more pipe involved and the boat is only 45ft long anyway. 

 

On the bypass valve - the Webasto manual and the folk at ButletTecknic recommend the two pipes/bypass valve to do what ChrisG says - micro air bubbles better expunged apparently.  

 

Well it's all a while off yet but the thinking bit is the bit that takes the longest...

 

They are obviously not plumbers or heating engineers!

Link to comment
Share on other sites

I filled both the engine and the Webasto central heating of my boat with Ford Premium 10 year antifreeze at a 50/50% mix.

 

The radiators refused to get hot unless I heated the radiators with a paint gun first. They then worked normally until the heating went off and they cooled down when I had to repeat the process. 

 

I drained the antifreeze and diluted it to a 25% mix and all worked normally, so too strong a mix causes heating issues.

 

 

  • Greenie 1
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.