Sunny day here but only getting 14.2v this morning from my 3 x 100w, in series, wired panels, normally about 57v in good sunshine.

12.1v and only 4.8A going into batteries,usually around 17A, and only 32% state of charge.

Batteries (720Ah) don't need topping up.

What's going on???

Link to comment
Share on other sites

check rhe connection between the first and second pannal,

Have you got your inverter on with a load being drawn,

I'd go one step further than Paul and check all your connections. (Donut anybody?)

Phil

Edited by Phil Ambrose
Link to comment
Share on other sites

My 4 panels are semi flexibles screwed flat to a cream roof. They normally give just over 80 volts but the last few days it has been between 80 and 62. I've put this down to the roof being rather warm.

Edited by pearley
Link to comment
Share on other sites

My 4 panels are semi flexibles screwed flat to a cream roof. They normally give just over 80 volts but the last few days it has been between 80 and 62. I've put this down to the roof being rather warm.

Are they 100 w panels?

Link to comment
Share on other sites

Sunny day here but only getting 14.2v this morning from my 3 x 100w, in series, wired panels, normally about 57v in good sunshine.

12.1v and only 4.8A going into batteries,usually around 17A, and only 32% state of charge.

Batteries (720Ah) don't need topping up.

What's going on???

They lose a bit of efficiency when it's hot.

Link to comment
Share on other sites

Check the labels on the panels and look for Voltage at P max probably in the region of 19.3v for a 100 watt panel.

 

So three panels (100 watt each) wired in series will give a maximum voltage , at the controller of 3*19.3 = 57.9v

 

Looking back you are getting this (almost) so your panels are OK.

 

So the low voltage was probably an outside influence as to what that was...


Pearley probably gets a higher voltage as his panels are possibly in the region of 36v P max. per panel depends on type.


I have 400 watts (19.3v Pmax) wired in series. parallel and the max. voltage at the controller is 38.6 v

Link to comment
Share on other sites

Check the labels on the panels and look for Voltage at P max probably in the region of 19.3v for a 100 watt panel.

 

So three panels (100 watt each) wired in series will give a maximum voltage , at the controller of 3*19.3 = 57.9v

 

Looking back you are getting this (almost) so your panels are OK.

 

So the low voltage was probably an outside influence as to what that was...

Pearley probably gets a higher voltage as his panels are possibly in the region of 36v P max. per panel depends on type.

I have 400 watts (19.3v Pmax) wired in series. parallel and the max. voltage at the controller is 38.6 v

Yes max Power voltage on mine is 17.8v

 

Low voltage was because it was early morning although it was gloriously sunny!

Link to comment
Share on other sites

Strangely had 2 separate peeps come up yesterday and ask basically the same question as the OP.

Remember Volts isn't Amps.

Need both for Watts.

You can have the potential but little power behind it.

Link to comment
Share on other sites

Check the labels on the panels and look for Voltage at P max probably in the region of 19.3v for a 100 watt panel.

 

So three panels (100 watt each) wired in series will give a maximum voltage , at the controller of 3*19.3 = 57.9v

 

Looking back you are getting this (almost) so your panels are OK.

 

So the low voltage was probably an outside influence as to what that was...

Pearley probably gets a higher voltage as his panels are possibly in the region of 36v P max. per panel depends on type.

I have 400 watts (19.3v Pmax) wired in series. parallel and the max. voltage at the controller is 38.6 v

For some reason I haven't take a note of the panels spec but the sellers website states maximum OPEN CIRCUIT voltage is 21v. With 4 of them wired in series that is, theoretically, 84 volts. But less when the batteries are actually charging, ie under load. Edited by pearley
Link to comment
Share on other sites

just a quick (possibly silly) thought about solar panels on hot roofs...

 

has anyone thought of trying to put the panels on some form of heat exchanger with canal water pumped through (via a small pump run from the panels)?

 

I wonder whether the performance increase from the panels would more than offset the load of running the pump.

 

of course another possible advantage would be that at least one area of the roof would be cool

Link to comment
Share on other sites

If max power is 17.8 x 3 that's 53.4v so at 57v your panels are over performing, happy days.

 

Neil

 

That is how they guarantee them to be 80% efficient after 10 years. rolleyes.gif

For some reason I haven't take a note of the panels spec but the sellers website states maximum OPEN CIRCUIT voltage is 21v. With 4 of them wired in series that is, theoretically, 84 volts. But less when the batteries are actually charging, ie under load.

 

Yes and that voltage should be in the v Pmax range if all things are correct, panels cool and the panels aligned with the sun correctly.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.