Fuse for 3000 w inverter


wullie

Featured Posts

I assume your Victron has a substantial internal fuse like mine, so the fuse you are installing is to protect the wiring between the batteries and the Victron and therefore should be related to the wire size, which is in turn related to the current you expect to take through it. Have I got that right?

I use a lower fuse than the wiring can take to check that I am not taking more than I expect to be ever needed.

Link to comment
Share on other sites

I assume your Victron has a substantial internal fuse like mine, so the fuse you are installing is to protect the wiring between the batteries and the Victron and therefore should be related to the wire size, which is in turn related to the current you expect to take through it. Have I got that right?

I use a lower fuse than the wiring can take to check that I am not taking more than I expect to be ever needed.

My 5 year old Victron Combi doesn't have an internal fuse.The one it replaced did.

Edited by pearley
Link to comment
Share on other sites

Not all inverters have fuses fitted DC or AC my Victron 3000 doesn't.

Are you talking about for inverter protection or cable protection?

 

Not all inverters have user accessible fuses, that's true. However, all inverter DC feeds (and/or charger outputs) should be fused to protect the cable.

Link to comment
Share on other sites

Where did Victron come from

 

There are plenty of other 3000 watt inverters out there

 

That came simply from the fact that I quoted the recommendation for our Victron unit.

 

Would you expect the necessary fuse rating to differ that much between inverters of the same rating? They're all going to draw about the same amount of DC current to supply 3kW AC, give or take a few % of efficiency.

Link to comment
Share on other sites

The fuse should reflect the cable capacity. If the cable can carry the required nearly 400 amps for full power use including any start surge ( most inverters are capable of 25% overload for a few seconds) then fit a 400A fuse, if using thinner cable, fuse to save the cable but carry spares as someone will probably switch two mains things on at once, thus exceeding the lower rating you have imposed on the inverter, causing the fuse to blow.

Link to comment
Share on other sites

It makes zero sense to wire an inverter with cable that's 'too small'. What happens when someone turns on a kettle while the DVD player and TV is on?

 

70mm2 should be fine for a 3kW inverter unless it is a long way from the batteries. A 400A fuse will protect a 70mm2 cable just fine.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.