I have been given a Nasa monitor BM1 model which has a 100amp shunt.Our boat has 4x110 leiure plus 1 x110 amp batteries.We also have a victron charger/inverter 1600 watts with i think from memory chargers at 70amp max.Engine is a Beta 38 twin alts i think 40 amp to starter and 75 amp to leisure batteries.My question is will the NASA monitor be ok to fit? Im not sure that the shunt is of sufficent capacity?

 

Cheers.

Link to comment
Share on other sites

I've got a nasa BM-1, 400Ah battery, 70A alternators, 800W inverter. The main problem you'll have is with the inverter. 1600W is well over 100A if running flat out. For short periods (seconds) the shunt would be ok, however it won't necessarily stand running full power continuously. Where the problem will come is in the BM-1 itself. It uses an integrator that feeds into an analogue input and this can get seriously out of sync for loads above its max design input. I've never had an issue but Gibbo suggested there is at least one unit on the market where exceeding the max threshold causes the calculation to become inverted (arithmetic overflow). The one we've got has issues with battery SoC and I mainly use it as a volt meter and ammeter, the battery SoC display being largely ignored.

Link to comment
Share on other sites

You really need a higher current shunt. The Victron Combi with its inverter running at max power will draw 150 amps or more.

 

We dont run the inverter at anywhere near max but i take your point.Do you know if its acceptable to use say a 200 amp shunt with a Nasa BM1? Also what would happen if we overloaded the shunt?

 

Cheers.

Link to comment
Share on other sites

The NASA BM2 has a 200 amp shunt but the manufacturers claim the shunts and wiring are not interchangeable with the BM1, although they are both standard 50mV (the voltage across the shunt at max rated current).

Link to comment
Share on other sites

I've never had an issue but Gibbo suggested there is at least one unit on the market where exceeding the max threshold causes the calculation to become inverted (arithmetic overflow).

 

It wasn't me. I do remember someone else saying that.

Edited by Gibbo
Link to comment
Share on other sites

The NASA BM2 has a 200 amp shunt but the manufacturers claim the shunts and wiring are not interchangeable with the BM1, although they are both standard 50mV (the voltage across the shunt at max rated current).

Isn't that why they're incompatable?

 

The BM1 equates 50mV as 100Amps

The BM2 equates 50mV as 200Amps

 

I bet there's something fairly simple inside them that makes the difference though

Link to comment
Share on other sites

There will be gain setting resistors on the sense amplifier that would have to be changed. They will be the size of ant shit.

 

Then the firmware in the micro processor would have to be changed. The firmware will be copy protected so you won't be able to read it out anyway, and even if you could, it would take 6 months to work out what needed changing.

Link to comment
Share on other sites

There is an opinion in the yachting world that the BM-1 will count in excess if 100Ah, but merely won't display over 100Ah. Similarly, the BM-2 will count in excess of 200Ah, but won't display.

 

A search of the forums on www.ybw.com would reveal the sources - I believe them to be well respected in engineering and electrical fields.

Link to comment
Share on other sites

Isn't that why they're incompatable?

 

The BM1 equates 50mV as 100Amps

The BM2 equates 50mV as 200Amps

 

I bet there's something fairly simple inside them that makes the difference though

OP could put a 75mV 150A shunt in, start about £6ish on Ebay. That will give 50mV at 100A but handle 150A no problem. Depends whether the BM is a working one and what it does when it sees >50mV on it's shunt input.

 

It might just read overload and not count it towards it's charge calculations, an email to their tech support might get the answer (and confirm it can't be converted to read 200A like a BM2)

 

Edit: Just read Richard10002's message above, sounds good.

 

cheers, Pete.

~smpt~

Edited by smileypete
Link to comment
Share on other sites

I don't know what margin of error is built in, but surely the greater possibility is that a 100 Amp shunt might not like having 150 Amps passed through it, rather than the monitor itself will get damaged if (say) 75 mV appears at the input.

 

Of course if you actually managed to completely burn the shunt out, then the monitor would end up seeing a lot more than 50 (or even 75) milliVolts, though. :o

Edited by alan_fincher
Link to comment
Share on other sites

The Victron 1600/70 combi if fitted with the battery monitor BMV 600 supplied by Victron comes with a 500A/50mV shunt,so does this indicate that a 100 amp shunt is advisable?

Edited by bowten
Link to comment
Share on other sites

I just checked a NASA BM1

 

It's a 50mV/100A shunt

 

Exceeding 50mV works for a small margin. It displays up to 104 amps then doesn't go any higher. It doesn't wrap around or do anything silly as someone else said they did.

 

The amp hour counter does not deal with anything higher than 104 amps. Despite what ybw say.

Link to comment
Share on other sites

I just checked a NASA BM1

 

It's a 50mV/100A shunt

 

Exceeding 50mV works for a small margin. It displays up to 104 amps then doesn't go any higher. It doesn't wrap around or do anything silly as someone else said they did.

 

The amp hour counter does not deal with anything higher than 104 amps. Despite what ybw say.

 

 

So would you think it ok to fit?

Link to comment
Share on other sites

So would you think it ok to fit?

 

Your inverter will overload it.

 

Good engineering practice dictates that nothing is ever run at maximum rated capacity. Only a fool does that. Yet for some reaosn people run 100 amp shunts at 100 amps. A proper engineer would never run one past about 65 to 70 amps. Your inverter will be way higher than even 100 amps.

Link to comment
Share on other sites

Your inverter will overload it.

 

Good engineering practice dictates that nothing is ever run at maximum rated capacity. Only a fool does that. Yet for some reaosn people run 100 amp shunts at 100 amps. A proper engineer would never run one past about 65 to 70 amps. Your inverter will be way higher than even 100 amps.

 

 

Thanks for your help,guess i shall have to buy one with a bigger shunt.I am suprised that NASA make these as they would appear to be to small to be of much use.

 

Cheers,

 

Ian.

Link to comment
Share on other sites

Thanks for your help,guess i shall have to buy one with a bigger shunt.I am suprised that NASA make these as they would appear to be to small to be of much use.

 

Cheers,

 

Ian.

 

Looking at the rest of the kit they sell I suspect it's geared towards the yachting fraternity where there's less reliance on the engine and consequently lower power consumption.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.