ISO 10239 contains the following design guidance for pressure drop:
sorry the table format has been lost, but you should be able to make sense of it.
I do not know what is the allowable pressure drop, no doubt someone will come along in a minute and clarify.
Annex A
Design guidelines for pressure drop due to pipe resistance
Pressure Pipes/hoses, drop, in kPa/m of pipe length:
inside diameter Connected appliance input
mm 1 kW 2 kW 3 kW 4 kW 6 kW 8 kW 10 kW 12 kW 15 kW
4 0,004 0,015 0,03 0,05 0,15 0,23 — — —
6 0,001 0,004 0,007 0,012 0,03 0,04 0,07 0,1 0,14
8 < 0,001 0,001 0,002 0,003 0,01 0,015 0,02 0,025 0,04
10 — < 0,001 < 0,001 0,001 0,003 0,004 0,006 0,009 0,013
13 — — — < 0,001 0,001 0,001 0,002 0,002 0,004
NOTE 1 This table is for use with propane at 3 kPa, 3,7 kPa and 5 kPa and butane at 3 kPa and 5 kPa.
NOTE 2 Equivalent lengths of pipe for fittings are:
tee and elbow 0,6 m,
straight connector 0,3 m,
hose or pipe bend 0,3 m.
NOTE 3 The volume of pipework should be minimized by using the smallest pipe sizes consistent with the pressure-drop
requirement.
EN ISO 10239:2000