Lee J Posted September 24, 2008 Report Share Posted September 24, 2008 Eventually I will be installing a combined Inverter/charger with auto changeover so my question is this: Do I fit one RCD to protect the shoreline and inverter, and then a second to give protection to the rest of the boat when not on shore power? Whilst on the subject, I intend putting a shoreline hook up at both ends of the boat. Can I then use a changeover switch to connect which ever one is plugged in to the system. Thanks Lee Link to comment Share on other sites More sharing options...
sociable_hermit Posted September 24, 2008 Report Share Posted September 24, 2008 Idleness posted this link in another thread. It's a good one for your question: http://www.smartgauge.co.uk/nb_ac_sys.html Link to comment Share on other sites More sharing options...
Guest steve newton Posted September 24, 2008 Report Share Posted September 24, 2008 Eventually I will be installing a combined Inverter/charger with auto changeover so my question is this: Do I fit one RCD to protect the shoreline and inverter, and then a second to give protection to the rest of the boat when not on shore power? Whilst on the subject, I intend putting a shoreline hook up at both ends of the boat. Can I then use a changeover switch to connect which ever one is plugged in to the system.Thanks Lee whoa lee. slow down... if you fit a second RCD surely it's a safety hazard? well... i suppose you CAN use a changeover switch for this purpose but if you're a true boating enthusiast then you wouldn't ruin your boat's integrity like that. why don't you get a biplug system? then a changeover switch won't be necessary? Steve.x Link to comment Share on other sites More sharing options...
Lee J Posted September 24, 2008 Author Report Share Posted September 24, 2008 Thanks for the speedy ones! Sadly Gibbo's diagrams don't show an inverter charger with integrated changeover, but it was seeing that thread that raised this question. Steve I'm not sure what you mean by challenging my boating enthusiasm, and struggle to understand the point about my boats integrity, I'm also unsure of what a biplug system is! Please could you clarify? Lee Link to comment Share on other sites More sharing options...
Nine of Hearts Posted September 24, 2008 Report Share Posted September 24, 2008 My inverter is protected via an RCD from the 240v shoreline, and then there's a distribution box with MCB's downstream of the inverter for the 240v supply to the boat. The inverter manual should specify the RCD you need and where to wire it, the instructions for mine (Mastervolt) were pretty explicit. Link to comment Share on other sites More sharing options...
Guest TerryL Posted September 24, 2008 Report Share Posted September 24, 2008 Eventually I will be installing a combined Inverter/charger with auto changeover so my question is this: Do I fit one RCD to protect the shoreline and inverter, and then a second to give protection to the rest of the boat when not on shore power? Whilst on the subject, I intend putting a shoreline hook up at both ends of the boat. Can I then use a changeover switch to connect which ever one is plugged in to the system.Thanks Lee Because you are using two diffent supplies in different circumstances, one from the shore and one from the boat, they both need an RCD to improve the electric shock safety on shore and onboard and both will be in use when on shore supply. A change over switch would need to be double pole so that the unused plug cannot become live. This can also be done at one end with a simple socket to connect into the further plug with a short lead when used. Link to comment Share on other sites More sharing options...
RobinJ Posted September 24, 2008 Report Share Posted September 24, 2008 whoa lee. slow down... if you fit a second RCD surely it's a safety hazard? well... i suppose you CAN use a changeover switch for this purpose but if you're a true boating enthusiast then you wouldn't ruin your boat's integrity like that. why don't you get a biplug system? then a changeover switch won't be necessary? Any system that involves connecting a boat to shore has potential hazard between the point where the connection is made and the RCD unit, thats why insulation is important. If you have a system that 'defaults to shore', ie only changes over when the generator or inverter is powered up, then I cannot see a problem, since the shore earth will be the most dangerous one, the generator or inverter will be earthed to the boat anyway! Link to comment Share on other sites More sharing options...
Guest TerryL Posted September 24, 2008 Report Share Posted September 24, 2008 My inverter is protected via an RCD from the 240v shoreline, and then there's a distribution box with MCB's downstream of the inverter for the 240v supply to the boat. The inverter manual should specify the RCD you need and where to wire it, the instructions for mine (Mastervolt) were pretty explicit. Slight misconception here, the RCD does not protect your equipment but protects persons with direct contact from electric shock and the cable, circuit and equipment from line earth faults. The MCB or fuses protect the cable, circuit or equipment from overload and provide the basic live to earth fault protection from electric shock. Your equipment can still draw a fault current unless the fuse or MCB becomes overloaded or an earth fault develops. Link to comment Share on other sites More sharing options...
Eeyore Posted September 25, 2008 Report Share Posted September 25, 2008 Eventually I will be installing a combined Inverter/charger with auto changeover so my question is this: Do I fit one RCD to protect the shoreline and inverter, and then a second to give protection to the rest of the boat when not on shore power? Whilst on the subject, I intend putting a shoreline hook up at both ends of the boat. Can I then use a changeover switch to connect which ever one is plugged in to the system.Thanks Lee The simple answer to your question is yes. The RCD in the consumer unit protects you from fault conditions in circuits and appliances connected to it. The RCD in the supply protects you from fault conditions in the inverter/charger. The question to other forum members is this - should there be individual RCD protection of each shore connection? Imagine the following: a single RCD is installed between the changeover arrangement and the inverter/charger. The shore line is then connected to the front of the boat whilst the changeover arrangement is set to the back position. Is it then acceptable to have an unprotected supply running the length of the boat from the front shore connector to the changeover arrangement? I accept that this condition would not be intentional, but is possible. The basis of this question is - should the operator (boat owner) be able to bypass or negate any part of the safety arrangements during any normal operation of the system? (Most of my experience has been with repair and upgrading of existing installations, and my personal preference in those circumstances has been to provide RCBO (combined RCD & MCB) at each source of supply.) Steve Link to comment Share on other sites More sharing options...
Gary Peacock Posted September 25, 2008 Report Share Posted September 25, 2008 From the regulations- 7.2.2 A manually reset trip-free circuit-breaker shall be installed within 0,5 m of the source of power or, if impractical, the conductor from the source of power to the panel-board circuit-breaker shall be contained within a protective covering, such as a junction box, control box, enclosed panel-board, or within a conduit or cable trunking or equivalent protective covering. If the location of the main shore-power inlet circuit-breaker exceeds 3 m from the shore-power inlet connection or the electrical attachment point of a permanently installed shore-power cord, additional fuses or circuit-breakers shall be provided within 3 m of the inlet or attachment point to the electrical system in the craft, measured along the conductor. Link to comment Share on other sites More sharing options...
Lee J Posted September 26, 2008 Author Report Share Posted September 26, 2008 From the regulations- 7.2.2 A manually reset trip-free circuit-breaker shall be installed within 0,5 m of the source of power or, if impractical, the conductor from the source of power to the panel-board circuit-breaker shall be contained within a protective covering, such as a junction box, control box, enclosed panel-board, or within a conduit or cable trunking or equivalent protective covering. If the location of the main shore-power inlet circuit-breaker exceeds 3 m from the shore-power inlet connection or the electrical attachment point of a permanently installed shore-power cord, additional fuses or circuit-breakers shall be provided within 3 m of the inlet or attachment point to the electrical system in the craft, measured along the conductor. Thanks for the replys, so Gary 3 RCD's! Lee Link to comment Share on other sites More sharing options...
Smelly Posted September 26, 2008 Report Share Posted September 26, 2008 Shouldn't there usually be an RCD on the shorepower supply anyway? Wouldn't it be less hassle to put one there instead of installing one before and one after the combo? You can buy commando sockets with inbuilt RCDs, (I think) wouldn't that be enough if you were trailing a cable down the garden friom the shed's supply? This sounds like needlessly complicating things to me! Link to comment Share on other sites More sharing options...
wonderdust Posted September 26, 2008 Report Share Posted September 26, 2008 Whilst on the subject, I intend putting a shoreline hook up at both ends of the boat.ThanksLee Or buy a longer shore power lead. Link to comment Share on other sites More sharing options...
Lee J Posted September 26, 2008 Author Report Share Posted September 26, 2008 Yes but I would still need one on the otherside of the inverter for when I'm not on shore power Link to comment Share on other sites More sharing options...
RobinJ Posted September 26, 2008 Report Share Posted September 26, 2008 Yes but I would still need one on the otherside of the inverter for when I'm not on shore power The simply way is to have a socket into which you plug, either the shoreline, generator or inverter etc. However if you plan to have a socket at each end of the boat, you need to ensure that two cannot be plugged in at the same time, thereby needing some sort of switching. Also as they are likely to be more than the requisite distance apart, proctection will be needed on at least one socket too (ie fuses). If installing a switching system, you will need to decide which socket has priority and which sources have priority over others, but you will probably end up with some expensive contactors and complicated wiring! Link to comment Share on other sites More sharing options...
Eeyore Posted September 26, 2008 Report Share Posted September 26, 2008 This sounds like needlessly complicating things to me! Quite true! But safety systems have evolved to protect those least able to appreciate the dangers. Don't forget we're talking about ordinary people who haven't a clue as to the dangers involved. Its a nanny state; sometimes you just have to bite your lip and get on with it. Steve Link to comment Share on other sites More sharing options...
Guest TerryL Posted September 26, 2008 Report Share Posted September 26, 2008 Yes but I would still need one on the otherside of the inverter for when I'm not on shore power There does seems to be confusion here so to clarify, you only need one RCD onboard if you have an invertor or generator, this will protect you from electric shock from either the inverter and generator and also when connected, the shore supply. Your marina, boatyard or any commercial shore supply is required to have an RCD at all outlets, this will protect you from electric shock involving the shore lead however it runs and also onboard at the outlets etc. if you have no onboard RCD fitted when using the mains supply. If both RCD's are the same rating then either or both can trip if an earth fault develops when on shore supply. Is that clear? Link to comment Share on other sites More sharing options...
Featured Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now