I`m going to be fitting a Victron 3000 inverter soon and could do with a little advise regarding cable size.
Reading the Victron manual they advise using 90mm2 cable for runs up to 5 mtrs and 120mm2 for runs between 5 and 10 mtrs,
my run is between 5 and 6 mtrs.
At present I have 70mm2 cable, as the inverter has 2+ and 2- terminals would it be possible to run another 70mm2 cable along side the original giving a total area of 140mm 2 ?
If so I presume both positive cables would need to go through the same battery isolator but be individually fused, at present there is a 250 amp fuse fitted, so I would need to fit a similar one in the new cable.
Any advise would be much appreciated.