What's wrong with this picture?


Featured Posts

Generally speaking a central heating pump should be at the point of lowest pressure in the system. This avoids any areas of negative pressure which may cause air to be sucked in.

 

I would put the pump on the low level return to a boiler.

 

The instructions which came with our Bolin stated that the pump should be fitted between the last rad and the stove.

 

The pump was the only bit that performed as expected when we turned our c/h on for the first time.

 

Richard

Link to comment
Share on other sites

Paul.

 

Allow me to 'dip my oar in'.

 

If you have as described ; 1 stove, 3 rads, one pump. There's not many things that would stop it working. Make sure things comply with:

 

1. Circulation in the same direction as the natural convection, i.e. out at top of stove, out at bottom of rads.

 

2. Pump wired and connected correctly. If it is a centrifrugal type the ouput is the 'tangental' one and the direction of rotation must appropriate to that. The input pipe to the centre of the circle probably opposite the motor.

 

3. The pump should be low down in the circuit to ensure no air will stay trapped in it.

 

4. A header tank on the highest part of the circuit, note the connecting pipe should ideally be one inch or so in diameter, fairly straight and simple. Air must be able to bubble up through this pipe without assistance.

 

5. If there is another 'high point' in the circuit an air bleeding device should be located there too.

 

John Squeers

Edited by John Orentas
Link to comment
Share on other sites

Hi Richard

 

Thanks for that, the heating is still not working.

 

:-(

 

Is that

 

STOVE ---- BOLIN PUMP ---  RAD #3 --- RAD #2 --- RAD #1

 

or

 

STOVE ---- RAD #1 --- RAD #2 --- RAD #3 BOLIN PUMP

 

?

 

The pump should be the last thing in the return pipe before the pipe connects to the boiler.

 

Remember that the pump is not as powerful as a domestic pump, someone once described it to me as annoying the water rather than circulating it. Our feed pipe from the boiler goes uphill immediately after the boiler for about 250 mm and then runs down hill to the first rad. At the apex of the incline I have an automatic air bleed valve and this is still chucking out the odd bit of air now and again. As I discovered it is asking a lot from the pump to cope with too many elbows especially if they are in the tappings to go to rads and in 15 mm to boot (but I don't want to talk about that). :o

 

Richard

Link to comment
Share on other sites

Ok

 

The Boiler (in the picture) is a calorifier for hot water, it is plumbed into the same system as the heating.

 

LATEST THINGS - I have moved the PUMP now down to between the boiler and the first radiator, it was a job and a half! (which included me getting rather wet).

 

I've bled all the rads, the pump is working and i'm just waiting till the stove cools down before I bleed it.....

 

I have 22mm pipes.

 

You can ignore the aldi boiler because right now its not in the circuit.

 

Thanks for all your help so far I'll keep you informed as to what happens.

Link to comment
Share on other sites

Paul

 

If the pipe in your picture from the boiler is from the top connection on the stoves boiler then this looks ok, the inlet to the pump is under the motor and is connected to the flow from the stoves boiler, and the outlet from the pump which is at right angles to the motor is connected to the rads. In this configuration you are pumping the flow (just for information) this should work once you have all the air out of the system. My only comment on this configuration is that the pump is having to handle the hottest water in the system, but it will still work ok.

Edited by Big COL
Link to comment
Share on other sites

The pipe to the left must be the oulet of the pump.

 

You said the pump was at the lowest part of the system !. It is connected to the top (output) of the stove. See my note about circulating as per natural convection, the top pipe of the stove you MUST make the output.

 

The photo indicates that the pump is at the top of the cicuit, it should be in the return.

 

Also air is likely to get trapped in the pump in that orientation. It couldn't be positioned worse.

 

John Squeers

Edited by John Orentas
Link to comment
Share on other sites

Paul

 

If the pipe in your picture from the boiler is from the top connection on the stoves boiler then this looks ok, the inlet to the pump is under the motor and is connected to the flow from the stoves boiler, and the outlet from the pump which is at right angles to the motor is connected to the rads. In this configuration you are pumping the flow (just for information) this should work once you have all the air out of the system. My only comment on this configuration is that the pump is having to handle the hottest water in the system, but it will still work ok.

 

Excellent Col, we'll get the stove going and give it a go I'm pretty sure the air is now out of the system after last night - I bled all the rads etc.

 

 

The pipe to the left must be the oulet of the pump.

 

You said the pump was at the lowest part of the system !.  It is connected to the top (output) of the stove.  See my note about circulating as per natural convection, the top pipe of the stove you MUST make the output.

 

The photo indicates that the pump is at the top of the cicuit, it should be in the return.

 

Also air is likely to get trapped in the pump in that orientation.  It couldn't be positioned worse.

 

John Squeers

 

Ok - John because its a LOT of work to sort it out I'll try it as it is - the thing is that if I have to put it on the bottom pipe I have to add ANOTHER 4 elbow bits and that is going to be even more money out of my ever decreasing bank account LOL.

 

When I bought the boat by the way, this is where the pump was, however it was just joined by two bits of rubber pipe which meant that the flow of water was blocked, hence it only worked once in a blue moon.

Link to comment
Share on other sites

John

 

On a pumped system natural convection does not apply, as you normally come out of the boiler and drop to low level behind the boiler and then run flow and return at low level, the rads and cal are just tappings off a large loop of 22 MM pipe. the pump can go anywhere in that loop as long as it is configured to keep the water moving in the correct direction. The only downside to pumping the flow is that the pump has to handle the hottest water on the system, the advantage of having the pump on the return after all the rads is the water has cooled a little.

If you were converting a gravity system where the flow is running at high level then yes you are then right about natural convection and the pump needs to be at low level on the return.

Link to comment
Share on other sites

If this doesn't work you could have air caught in the first elbow on the outlet side of the pump. I had this problem but i know a man who knows and he went straight to it. With the pump not running he cracked the joint and air and water came out. Problem solved.

 

Incidentally, the advice to put the pump in the return came from Bolin, but what do they know :o

 

Richard

Edited by Rick
Link to comment
Share on other sites

Hi Richard

 

Yes - good advice, I will take it but I have to get to HOME BASE, I'm pretty sure you're right about the air lock. Only because the heat convects up to the pump and no further..... I'll do it this evening before we get the stove going and I get VERY hot water all over me :-)

 

The problem is that the bottom pipe I'll have to cut and add 4 elbow joints...oh dear...

Edited by clevett
Link to comment
Share on other sites

Sorry, folks, I've just re-read my post above. It is wrong!!! (just testing)

 

The pump should ideally be at the point of HIGHEST pressure with it running which usually means at a low point before an item of resistance eg a boiler.

 

The idea is to maintain positive pressure throughout the circuit so that air cannot get sucked in.

Link to comment
Share on other sites

Sorry, folks, I've just re-read my post above. It is wrong!!! (just testing)

 

The pump should ideally be at the point of HIGHEST pressure with it running which usually means at a low point before an item of resistance eg a boiler.

 

The idea is to maintain positive pressure throughout the circuit so that air cannot get sucked in.

 

So am I right?

Link to comment
Share on other sites

Timbo

 

1 Why would the highest pressure be at the lowest point?

 

2 What positive resistance does a boiler cause bearing in mind that on most systems on boats the pump is overrated for the boiler performance and usually need slowing down.

 

3 On a closed system that has had the air evacuated from it how does the pump suck air in any opening in the system will leak water?.

Link to comment
Share on other sites

When the pump is not running the point of highest pressure will be at the low point of the system due to the static head. There will be no resistance in the circuit because no fluid is flowing.

 

Once the pump is running it effectively "adds" pressure across itself but the various resistances in the circuit act as negative heads.

 

If all the pressures around the circuit are positive then the system will tend to leaking rather than sucking in air. If it was sucking in air , you would not see a leak.

 

If all the joints are 100% then no air should get in anyway, but it is much easier for air to get in than for water to get out through a tiny imperfection.

 

If the pump was in the wrong position and the flow rate was extremely high (unrealistic) then it would be possible for air to get in through the header tank.

 

I advise putting the pump at the low point in the boiler return before the boiler.

Link to comment
Share on other sites

Right....

 

I've spent the last 4 days moving this pump around, its been High, Low, on the send and return and the rads are still cold.

 

I'm not jolly moving it again unless someone can give me a real reason why and what to do next.

 

Every move costs money because I have had to replace the old elbow joints and t-pieces.

 

Has anyone got a Bolin Pump manual? if its not too HUGE theres no chance it could be scanned and emailed?

Link to comment
Share on other sites

Paul

 

If you still have no heat in the rads then there is something else on the system causing a problem, either there is air trapped somewhere, or there is a problem with the pipe work where you bypassed the gas boiler, because as you describe the system set up it should work.

Its difficult to work out whats going on not having seen the pipe work so can we establish some basic facts and then go on from there

 

1 With the pump running and the stove running are you getting hot water on the return to the stove. ie the pipe that comes into the bottom of the stoves boiler.

 

2 If there is no hot water on the return how far is the hot water getting on the flow ie the top pipe out of the boiler.

 

Forget about the pump pumping air, this is a flooded system if there where any places that air could get in then it will leak water when the pump is not running. The pump is only there to move the water round a loop, air in the system is the most common cause, it gets trapped in places you would least expect I have had enough experience with this problem so know the problems well enough. Don't get disheartened you will get through this.

Link to comment
Share on other sites

Hi Colin

 

LATEST

 

Got home took the Bleed valve off the back boiler and lo and behold the pipe was nearly empty so I filled it with water and put the bleeder back on.

 

I'm now running up the fire to see what happens, but there was a second where the hot water appears to have moved through the system. (the stove was coldish).

 

17:35 UPDATE: 1/2 hour later pipes and rads appear to be warming but very slowly so I've ramped up the stove to see what happens.

Edited by clevett
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.