That makes sense.
However, why does this not apply when connecting the two ends of a ring to a single fuse?
If a ring was inadvertently broken this would, in effect, convert it into two seperate radials. The circuit and appliances attached would remain in working order, drawing as much current as before, without any indication that anything is untoward. The two radials would run to a single fuse, rated at twice their capacity. Thus there is the possibility, that either radial could exceed its rated capacity.
For example, a household 32A mains circuit runs from a single fuse to a ring made up of 16A cable. This is fine, unless there is a break part-way round the ring. Three 10A sockets now on one side of the break, could draw 30A across the 16A rated cable, where previously this would have been shared across both sides of the ring.