Inverter to RCD, advice please


Featured Posts

Hi all,

 

Have finally gotten around to servicing engine 'ole, repainting bilge, rewiring.

 

We don't have shoreline. I want to protect the single 240 circuit with a separate RCD. Currently, it just has a 150A fuse on the 12V side.

 

I'm unsure what to do with the earth. Do I run it straight into the inverter, and subsequently to the hull via the 12V negative?

 

TIA

Link to comment
Share on other sites

Hi all,

 

Have finally gotten around to servicing engine 'ole, repainting bilge, rewiring.

 

We don't have shoreline. I want to protect the single 240 circuit with a separate RCD. Currently, it just has a 150A fuse on the 12V side.

 

I'm unsure what to do with the earth. Do I run it straight into the inverter, and subsequently to the hull via the 12V negative?

 

TIA

Cut from a post of yours eariyer today......Inverters are cheap and easy enough. Could be integrated with existing 240v system via a fusebox.

Not so easy 'mbee? By earth are you refering to 12V negative to inverter or 240v ?
Edit. Slow typeing, WotEver has picked up and pointed you in the right direction. Good.
Edited by Taslim
  • Greenie 1
Link to comment
Share on other sites

 

Cut from a post of yours eariyer today......Inverters are cheap and easy enough. Could be integrated with existing 240v system via a fusebox.

Not so easy 'mbee? By earth are you refering to 12V negative to inverter or 240v ?
Edit. Slow typeing, WotEver has picked up and pointed you in the right direction. Good.

 

 

 

:D

 

Having seen the diagram, I'd stand by what I said....adding a small inverter is easy enough. The other thread coincided with what I was doing...admittedly, I hadn't given too much thought to the RCD yet. All I was unclear on was if the RCD required a separate bond to the hull, or, if the inverter was arranged to be able to use the 12V connection to the hull. Reading previous threads, there does seem to be some uncertainty on this. Ultimately, it isn't difficult to do - which was what I was saying. Perhaps I should remain quiet.

 

I don't claim to be a genius - so asked for specific advice. Having considered it, I suppose I wouldn't want a fault load to be directed through the inverter/batteries to the hull, nor am I certain it could be. Glad I asked though!

Link to comment
Share on other sites

 

 

biggrin.png

 

Having seen the diagram, I'd stand by what I said....adding a small inverter is easy enough. The other thread coincided with what I was doing...admittedly, I hadn't given too much thought to the RCD yet. All I was unclear on was if the RCD required a separate bond to the hull, or, if the inverter was arranged to be able to use the 12V connection to the hull. Reading previous threads, there does seem to be some uncertainty on this. Ultimately, it isn't difficult to do - which was what I was saying. Perhaps I should remain quiet.

 

I don't claim to be a genius - so asked for specific advice. Having considered it, I suppose I wouldn't want a fault load to be directed through the inverter/batteries to the hull, nor am I certain it could be. Glad I asked though!

I wasn't taking a pop. closedeyes.gif Just noticed the two threads.

 

You were quite right to ask even if only to confirm what you already knew.

Link to comment
Share on other sites

All I was unclear on was if the RCD required a separate bond to the hull, or, if the inverter was arranged to be able to use the 12V connection to the hull. Reading previous threads, there does seem to be some uncertainty on this

Phrased as above, I'm somewhat confused that you refer to previous threads having 'some uncertainty'.

 

The output of the GI or IT and/or Inverter goes to the consumer unit, possibly via a changeover switch. Within the CU is an RCD, the output of which feeds MCBs which in turn feed the 230V around the boat. The consumer unit should have a cable, at least 4mm2 which bonds the earth rail in the CU to the hull. The hull connection should ideally (for ease of understanding for future users) be adjacent to but separate from the 12V -ve bond.

 

No confusion or uncertainty.

 

Tony

 

Of course, the inverter also requires a N-E bond at its output for the RCD to operate correctly.

"at its output" can mean internal depending on the manufacturer.

Link to comment
Share on other sites

Phrased as above, I'm somewhat confused that you refer to previous threads having 'some uncertainty'.

 

The output of the GI or IT and/or Inverter goes to the consumer unit, possibly via a changeover switch. Within the CU is an RCD, the output of which feeds MCBs which in turn feed the 230V around the boat. The consumer unit should have a cable, at least 4mm2 which bonds the earth rail in the CU to the hull. The hull connection should ideally (for ease of understanding for future users) be adjacent to but separate from the 12V -ve bond.

 

No confusion or uncertainty.

 

Tony

 

Of course, the inverter also requires a N-E bond at its output for the RCD to operate correctly.

"at its output" can mean internal depending on the manufacturer.

Pretty much the way I did ours. Always worth checking with manufacturer before adding N-E bond. My Sterling had no such bond, but on checking it was OK to install one. It tripped instantly when a running power tool went for a swim recently.

Link to comment
Share on other sites

Green things all round.

 

Now that we're over the initial hurdles, I'm focussing (and learning) on safety. There is no apparent N-E point on the inverter, but I'll take a look at the manufacturer's guidelines.

 

:D

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.