Featured Posts

Is it a reasonable suggestion to supplement the existing alternator/ battery charging with additional input from an external battery charger supplied from my dometic alternator or would they balance each other out and I end up with the same charging rate? Engine Barrus 45 with 3 alternators and smartbank split charge system installed.

Link to comment
Share on other sites

If you have a charger on board it allows you to charge if something fails in the normal charging system(alternator) and, depending on the charger, may allow you increase the voltage from time to time for an equalise charge.

 

Otherwise I agree with Chris, it won't end up charging your batteries significantly quicker if you use the sources of charge all at the same time - well, unless the battery bank is very large and/ or the alternators are very small.

Edited by nicknorman
Link to comment
Share on other sites

Is it a reasonable suggestion to supplement the existing alternator/ battery charging with additional input from an external battery charger supplied from my dometic alternator or would they balance each other out and I end up with the same charging rate? Engine Barrus 45 with 3 alternators and smartbank split charge system installed.

 

Not sure how you intend to power a battery charger from your domestic battery alternator but in any case need a bit more info to answer your question comprehensively:

 

Output of each of your three alternators? Number and size of batteries/banks? What heavy loads you put on your main service bank? - inverter supplying washing machine for example.

 

There is a limit to how much current you can squeeze into a battery bank at any particular point in the charge cycle, above which charge times won't be significantly reduced, as suggested above. However if you intend to run say a washing machine from batteries via inverter then extra current from the alternators will always help.

 

Redundancy by using at least two of your three alternators to supply the main service bank ought to be sort as well in case one goes down.

Link to comment
Share on other sites

Not sure how you intend to power a battery charger from your domestic battery alternator but in any case need a bit more info to answer your question comprehensively:

 

Output of each of your three alternators? Number and size of batteries/banks? What heavy loads you put on your main service bank? - inverter supplying washing machine for example.

 

There is a limit to how much current you can squeeze into a battery bank at any particular point in the charge cycle, above which charge times won't be significantly reduced, as suggested above. However if you intend to run say a washing machine from batteries via inverter then extra current from the alternators will always help.

 

Redundancy by using at least two of your three alternators to supply the main service bank ought to be sort as well in case one goes down.

I had presumed that when he said 3 alternators, one was a TravelPower but I could be wrong!

Link to comment
Share on other sites

I had presumed that when he said 3 alternators, one was a TravelPower but I could be wrong!

 

Yes that makes sense although the OP did mention powering a (mains?) battery charger from the domestic alternator.

 

If that's the case then such a charger would allow extra charge current if and when its was needed. I believe you use yours in a similar manner Nick.

 

ETA: ho hum - just re-read Dometic blush.png

Edited by by'eck
Link to comment
Share on other sites

Yes that makes sense although the OP did mention powering a (mains?) battery charger from the domestic alternator.

 

If that's the case then such a charger would allow extra charge current if and when its was needed. I believe you use yours in a similar manner Nick.

 

ETA: ho hum - just re-read Dometic :blush:

Oh yes, I missed the missing "s" as well! If we put the TravelPower on, it automatically feeds the Mastervolt Combi so can charge the batteries, however whether any current flows depends on the Combi voltage settings and battery temperature. I think that the 175A main alternator is plenty for a 440AH bank so don't try to force more in. What I sometimes do is to increase the Combi voltage near the end of the charge to do a bit of an equalisation over-charge - the batteries seem to like that!

Link to comment
Share on other sites

Is it a reasonable suggestion to supplement the existing alternator/ battery charging with additional input from an external battery charger supplied from my dometic alternator or would they balance each other out and I end up with the same charging rate? Engine Barrus 45 with 3 alternators and smartbank split charge system installed.

I have 450 amp Trojan battery bank with 175amp alternator and 3.5kva travel power.I have recently stopped using the 175amp alternator and just use the T/P through a Victron charger which is a 1600/70/12.I find the batteries will be more cared for in this setup rather than using the alternator and the charger together.

Link to comment
Share on other sites

I have 450 amp Trojan battery bank with 175amp alternator and 3.5kva travel power.I have recently stopped using the 175amp alternator and just use the T/P through a Victron charger which is a 1600/70/12.I find the batteries will be more cared for in this setup rather than using the alternator and the charger together.

You have therefore reduced your maximum charging current from 175A to 70A. How do you find the time taken to fully recharge compares pre- and post- this change?

Link to comment
Share on other sites

Lots depends on the life style that you live.

If you cruise for 6 engine hours a day then you may need little to supplement this, If you moor til the batteries are flat then big solar is a good answer.

 

I would always have a selection of charge methods, including charger from shoreline and maybe a petrol genset for emergency use. Also the start battery could have a SMALL solar panel regardless

Link to comment
Share on other sites

You have therefore reduced your maximum charging current from 175A to 70A. How do you find the time taken to fully recharge compares pre- and post- this change?

 

I have found that charging the batteries from the multi, supplied by the standalone generator is more effective/quicker than using the engine alternator.

 

Alternator is 24v, 80 amp. multi is 24v 50 amp charger.

 

Alternator charges at 28.8v, multi charger at 29.2v (temperature compensated)

Link to comment
Share on other sites

Mike

 

Not authoritative in any way but my understanding and it may be wrong, is that when charging from two sources if not matched (voltage output ?) one of them will shut down.

 

There you are clear as mud. help.gif

Link to comment
Share on other sites

Mike

 

Not authoritative in any way but my understanding and it may be wrong, is that when charging from two sources if not matched (voltage output ?) one of them will shut down.

 

There you are clear as mud. help.gif

 

Maybe not shut down but go into idle, and then only when the max charge voltage of the source with the lowest setting is achieved.

Link to comment
Share on other sites

 

Maybe not shut down but go into idle, and then only when the max charge voltage of the source with the lowest setting is achieved.

Yes, and the regulation is fairly "soft" so that in absorption, as the voltage of the charger is adjusted (if your charger allows that) the proportion of current being supplied by the alternator vs the charger changes over a relatively wide range of voltages - in other words it doesn't suddenly flip from being supplied by the alternator, to the charger, or vice versa.

 

Back to OP's point, it depends on the power of the 12v alternators. Presuming they are fairly large, especially in combination, I don't think adding the charger output will make any difference to the charging time, because the batteries won't be able to absorb the extra current available quickly enough. Its likely to come out of bulk almost immediately. But as I mentioned, the ability to be able to do an equalise charge is a useful one, and a charger gives you more redundancy of supply.

Edited by nicknorman
Link to comment
Share on other sites

Is it a reasonable suggestion to supplement the existing alternator/ battery charging with additional input from an external battery charger supplied from my dometic alternator or would they balance each other out and I end up with the same charging rate? Engine Barrus 45 with 3 alternators and smartbank split charge system installed.

 

If you fit a simple ammeter for a few quid, or even a monitor like a NASA BM 1 or 2, for a hundred quid or so, you would be able to see the differences at different points in the charging process.

Link to comment
Share on other sites

Mike

 

Not authoritative in any way but my understanding and it may be wrong, is that when charging from two sources if not matched (voltage output ?) one of them will shut down.

 

There you are clear as mud. help.gif

 

Maybe not shut down but go into idle, and then only when the max charge voltage of the source with the lowest setting is achieved.

I thought this would be the case I just wanted to here the news from more knowledgeable source(s). Looks like battery charger on its own via my Honda then. Unless someone advises differently?

 

Many thanks Mike

Link to comment
Share on other sites

You have therefore reduced your maximum charging current from 175A to 70A. How do you find the time taken to fully recharge compares pre- and post- this change?

I haven't used the 175 amp alt with these batteries(Trojan 6v) only the T/P and Victron Charger.I am not sure I want such to use the 175 amp alt on these batteries because I am sure it killed my previous leisure batteries.I think by using the mains charger the Trojans will be better cared for even if I am using slightly more fuel to do so.

Link to comment
Share on other sites

I haven't used the 175 amp alt with these batteries(Trojan 6v) only the T/P and Victron Charger.I am not sure I want such to use the 175 amp alt on these batteries because I am sure it killed my previous leisure batteries.I think by using the mains charger the Trojans will be better cared for even if I am using slightly more fuel to do so.

Interesting - you mean killed them because the current was too high, or because of something to do with the voltage?

Link to comment
Share on other sites

With the 1% charging rule a battery can safely take a charging amperage of 1amp for each 1% of its depth of discharge (DoD) i.e. with a 200ah batt =100 amps can go into it @ 50% DoD, 80amps@ 40% DoD etc. At acceptance voltage (approx 80% SoC) battery will dictate the amount. So with a 175amp charger, any less than 875ah of battery will, in theory, run a risk of exceeding this rule when in bulk charge.

 

In practice we hammer our batts nuts off.

Edited by nb Innisfree
Link to comment
Share on other sites

With the 1% charging rule a battery can safely take a charging amperage of 1amp for each 1% of its depth of discharge (DoD) i.e. with a 200ah batt =100 amps can go into it @ 50% DoD, 80amps@ 40% DoD etc. At acceptance voltage (approx 80% SoC) battery will dictate the amount. So with a 175amp charger, any less than 875ah of battery will, in theory, run a risk of exceeding this rule when in bulk charge.

In practice we hammer our batts nuts off.

We've got 440Ah, so at 50% that's 220A according to your formula. In practice I find that initial 175A current starts to reduce fairly quickly (ie bulk phase ends pretty quickly) so not convinced we are exceeding your rule of thumb limit. In any case, there is a bit of a compromise to be had between maximising battery longevity and not consuming more fuel than necessary,if you have to run the engine just to charge the batteries. People do talk about a 20 or 25% charger to battery capacity ratio which we obviously exceed, but I haven't found any hard data that shows how much more rapidly life is consumed by fast charging.

Link to comment
Share on other sites

We've got 440Ah, so at 50% that's 220A according to your formula. In practice I find that initial 175A current starts to reduce fairly quickly (ie bulk phase ends pretty quickly) so not convinced we are exceeding your rule of thumb limit. In any case, there is a bit of a compromise to be had between maximising battery longevity and not consuming more fuel than necessary,if you have to run the engine just to charge the batteries. People do talk about a 20 or 25% charger to battery capacity ratio which we obviously exceed, but I haven't found any hard data that shows how much more rapidly life is consumed by fast charging.

Yes I agree, theory and practicality and all that. Also we are talking about batt capacity when

new, we have 480 ah @24v but possibly down to half that now, so we have 100

amps going into 240ah and we have survived so far! When our batts were new we would sometimes be in bulk charge and at full output for an hour or so if batts were well discharged.

 

Just to add, it's not my theory but taken from Gibbo's Smartgauge site.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.