Fridge problem


GUMPY

Featured Posts

My larder fridge seems to be running 24/7.  Normally I would suspect low refrigerant however there is ice forming on the back of the fridge which if it was not cooling obviously wouldn't happen. My suspicion is that the thermostat has gone. 

What does the team think?

 

 

 

 

I will be taking fridge home and testing with a probed external stat to see what happens.

Edited by Loddon
Link to comment
Share on other sites

26 minutes ago, Tracy D'arth said:

Why take it home? All you need is a multimeter.

Because I don't want to dismantle the fridge to get at the stat, if it is the stat at fault then I won't replace it I will use the external stat.

Link to comment
Share on other sites

1 minute ago, Tracy D'arth said:

Temperature will be erratic with the stat outside the cabinet.   How will you get the phial into the evaporator box?

 

Tempted to say via  hole drilled through the inner and outer skin and insulation all bunged up with two great blobs of mastic. As I used to see on the old three-way Electrolux.

Link to comment
Share on other sites

Temp probe will enter through the drain hole, no drilling required. Using This type of stat is a well known mod to give better temperature regulation. Stat runs from 12v and will switch 230v.

 

 

Edited by Loddon
Link to comment
Share on other sites

46 minutes ago, Loddon said:

Temp probe will enter through the drain hole, no drilling required. Using This type of stat is a well known mod to give better temperature regulation. Stat runs from 12v and will switch 230v.

 

 

Oh, that complicated. Thought you were using a capillary stat not a temperature controller.

Link to comment
Share on other sites

What type of fridge?  If a Shoreline 12v fridge, ring their tech support - very good and helpful, their test advice  & part fixed our 15 year old fridge.

 

Following their advice I rapidly ruled out a thermostat problem.    They've experienced very very few coolant leaks, other possibility was control unit.  Unit couriered next day on sale or return, fixed problem.

  • Greenie 1
Link to comment
Share on other sites

15 hours ago, Tracy D'arth said:

Oh, that complicated. Thought you were using a capillary stat not a temperature controller.

 

More concerning is the 3W constant power consumption. 

 

I know a lot of boaters don't consider 1/4A a lot, but its 24/7/365 just to turn the fridge on and off 

Link to comment
Share on other sites

14 hours ago, Loddon said:

It's a standard LEC mains fridge nothing exotic and ten years old. It replaced a ,12v fridge that lost its R12 😱

 

 

It is not your thermostat!

 

If it was, you would have also noted the contents of the fridge were far colder than usual.

Milk or water etc would be frozen solid.

If continuous running, with some ice still forming, is your only symptom, then you have lost some refrigerant.

That means you have a leak within the sealed system.  That can only get worse and eventually the ice will  stop forming.

It is not normally economical to repair, and cheaper to replace the refrigerator.

You will also be wasting your money playing around with alternative thermostats in the meantime.

Link to comment
Share on other sites

4 hours ago, Rebotco said:

 

It is not your thermostat!

 

If it was, you would have also noted the contents of the fridge were far colder than usual.

Milk or water etc would be frozen solid.

If continuous running, with some ice still forming, is your only symptom, then you have lost some refrigerant.

That means you have a leak within the sealed system.  That can only get worse and eventually the ice will  stop forming.

It is not normally economical to repair, and cheaper to replace the refrigerator.

You will also be wasting your money playing around with alternative thermostats in the meantime.

Interesting point and one to consider. It's in the back of the car and halfway home (I've stopped for a break) it will go in my workshop for the next few weeks on the 230v  stat that I have already to see how it does.  If it fails then decision to be made whether to go for a fridge or a freezer with an external stat which is way more efficient than a fridge.

 

ETA the only evidence I have of continuous running is C telling me it is as I can't hear it 😉

Edited by Loddon
Link to comment
Share on other sites

2 hours ago, Loddon said:

Interesting point and one to consider. It's in the back of the car and halfway home (I've stopped for a break) it will go in my workshop for the next few weeks on the 230v  stat that I have already to see how it does.  If it fails then decision to be made whether to go for a fridge or a freezer with an external stat which is way more efficient than a fridge.

 

ETA the only evidence I have of continuous running is C telling me it is as I can't hear it 😉

 

If you find it is not continuously running, and is cooling, then that's what it is supposed to do!!

Link to comment
Share on other sites

Shirley an easy way to test a 'stat 'specially one from Bognor unless they've boved it so change the setting porgreaaively to max temperature whille it's running. If it doesn'stop running it's probably a duff thremostat.

I did than on my aged Batts / Lec unit and it sduddenly started doing what it oughta'

Link to comment
Share on other sites

DEFROST it!

The ice is acting as an insulator, not allowing the cold from the refrigerant to reach the main body, which warms up to the point of the thermostat working correctly.

 

Bod

2 minutes ago, Loddon said:

Its sitting in the garage its internal stat set at #2 drawing 45W on my wattmeter i will watch what happens.

Hopefully it will work as normal  

If a lot of the ice has melted, it will work as normal, till the ice builds up again.

 

Bod

Link to comment
Share on other sites

12hrs later and it is down to temperature 3.5degC running on the external stat. However according to the meter it has consumed just over 0.5kWh in that period which means it hasn't been off for very long as it draws 45W when running (12hrx45w=540Wh)

Trying another 12hr run now it's down to temp to see how much it uses I would hope it's about 1/2 of that.

Edited by Loddon
Link to comment
Share on other sites

Three hours further on it is still running all the time even on the external stat and wont cool below 4.5degC.

Conclusion is that although the internal stat is a bit iffy the fridge has lost refrigerant so it will be on its way to the tip next time I go.

New one ordered same make and model will be here Saturday.

 

Some thoughts:

Surprised it only draws 45W I would have expected more as its rated at 70W in the spec, will be checking new one on arrival.

Compressor fire up showed 550W on the meter so  12 times consumption

Official consumption figures are 110kWh/Y or 304Wh/d, it drew over 0.5kWh in 12hrs so slightly high.

External stat draws 0.8W so I will have no problem leaving that on 24/7 on the boat ;)

 

 

 

 

Link to comment
Share on other sites

6 minutes ago, Sea Dog said:

Electric motor starting current is typically 5 - 7 times the running current.

Depends entirely on the motor. ;)

 

The rated wattage of the fridge is 70W so 550 is not far off. When the fridge started it peaked at 550 then dropped to about 70 before settling on 45 once it was running.

Edited by Loddon
Link to comment
Share on other sites

I use mine to chill my beer, or gin, I keep the glasses in the freezer box, it takes 30 minutes to get a decent drink. That's all that matters.

My fridge is  absolutely ancient, and I tried to use it normally, but gave up.

Link to comment
Share on other sites

  • 2 months later...
On 25/06/2022 at 14:41, Loddon said:

My larder fridge seems to be running 24/7.  Normally I would suspect low refrigerant however there is ice forming on the back of the fridge which if it was not cooling obviously wouldn't happen. My suspicion is that the thermostat has gone. 

What does the team think?

 

I will be taking fridge home and testing with a probed external stat to see what happens.


Our 11 year old Shoreline has been gradually getting worse over the past 3 years or so. I put an hour counter on the back and it was running roughly 75% of the time even in average weather. It was on constantly in the summer heat. Plenty of frost and ice on the evaporator panel though.

 

Anyway I decided to re-gas it. It is R134a which, despite being a replacement for bad ozone depleting refrigerants, now has a bad name and so no-one would re-gas it. So I did some research and bought a kit from ebay, R134a substitute, compatible.
 

Also found info that a symptom of low gas is excessive icing. Which seems counter-intuitive but it is to do with the reduced boiling point of the refrigerant when the pressure is less. Maybe it’s that it gets too cold which causes ice build up which acts as an insulator? 

 

Anyway, I added some refrigerant to take the running pressure on the inlet/low pressure side up to slightly positive, and now the fridge is much better. Just checked it over 24hrs and it ran about 35% of the time. Only down side is that it seems to gurgle more than it did, maybe the interaction of the two different refrigerants. But I can live with that!

Link to comment
Share on other sites

2 minutes ago, nicknorman said:

Only down side is that it seems to gurgle more than it did, maybe the interaction of the two different refrigerants.

We have a tall Indesit fridge jobby at home.  That too is prone to being noisy, but the makers helpfully included a booklet describing its various burps, farts and gurgles!

 

N

Link to comment
Share on other sites

29 minutes ago, nicknorman said:


Our 11 year old Shoreline has been gradually getting worse over the past 3 years or so. I put an hour counter on the back and it was running roughly 75% of the time even in average weather. It was on constantly in the summer heat. Plenty of frost and ice on the evaporator panel though.

 

Anyway I decided to re-gas it. It is R134a which, despite being a replacement for bad ozone depleting refrigerants, now has a bad name and so no-one would re-gas it. So I did some research and bought a kit from ebay, R134a substitute, compatible.
 

Also found info that a symptom of low gas is excessive icing. Which seems counter-intuitive but it is to do with the reduced boiling point of the refrigerant when the pressure is less. Maybe it’s that it gets too cold which causes ice build up which acts as an insulator? 

 

Anyway, I added some refrigerant to take the running pressure on the inlet/low pressure side up to slightly positive, and now the fridge is much better. Just checked it over 24hrs and it ran about 35% of the time. Only down side is that it seems to gurgle more than it did, maybe the interaction of the two different refrigerants. But I can live with that!

A friend recently re-gased one for me. Great fun.

IMG_20220808_113141835_HDR.jpg

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.