Isolation transformer buzz with generator


Jaston10078

Featured Posts

Hi there, 

 

Can anyone fathom a guess as to what is happening to cause the excessive transformer buzz that has recently started happening when we charge with our generator (a cheaper Honda copy) ? Video in link below... 

 

The buzzing gets worse the closer the genny is to the transformer... Is it some kind of interference? 

 

We also get a worrying knocking sound from the transformer under higher loads in bulk charge. 

 

Any help would be much appreciated. 

 

James 

 

 

Link to comment
Share on other sites

The waveform of the gen is not very pure. A pure side wave has very few harmonics but a square wave has lots of odd harmonics. The transformer expects to get a clean sine wave, modified sine wave can be a mix of square and triangular wave forms.

Its the same reason why microwave ovens demand a very pure sine wave.

Edited by Tracy D'arth
Link to comment
Share on other sites

8 minutes ago, Jaston10078 said:

Hi there, 

 

Can anyone fathom a guess as to what is happening to cause the excessive transformer buzz that has recently started happening when we charge with our generator (a cheaper Honda copy) ? Video in link below... 

 

The buzzing gets worse the closer the genny is to the transformer... Is it some kind of interference? 

 

We also get a worrying knocking sound from the transformer under higher loads in bulk charge. 

 

Any help would be much appreciated. 

 

James 

 

 

It seems that it's only when the charger is working... Any other large load like our immersion heater doesn't cause this... 

The immersion heater is a non inductive load, just resistance. AC current will induce eddy currents and physical stress in inductive loads like transformers, DC does not.

 

Not a daft question but why do you feed the gen into the transformer when you are charging batteries? The gen is either isolated or grounded with an earth spike so you don't have to have a transformer in circuit.

Link to comment
Share on other sites

The transformer is buzzing because it does not much like the output from the generator.  If you look at most small generator output with an oscilloscope there are lots of harmonics in the waveform and it is generally nothing like the pure even sine wave that the national grid delivers.  Cheap inverter generators can be among the worst.  As Tracy says, you don't need the IT on a generator, so if you can, take it out of circuit.

 

N

Link to comment
Share on other sites

Also your transformer will have bee designed to operate in a certain frequency band, likely 50 Hz to 60Hz and the generator may well be producing current outside this range.
I would think that you are not doing the transformer much good if its honking.

Link to comment
Share on other sites

2 hours ago, Tracy D'arth said:

Also your transformer will have bee designed to operate in a certain frequency band, likely 50 Hz to 60Hz and the generator may well be producing current outside this range.
I would think that you are not doing the transformer much good if its honking.

No generator should be more than a percent or two off 50Hz.

 

2 hours ago, Tracy D'arth said:

The immersion heater is a non inductive load, just resistance. AC current will induce eddy currents and physical stress in inductive loads like transformers, DC does not.

 

Not a daft question but why do you feed the gen into the transformer when you are charging batteries? The gen is either isolated or grounded with an earth spike so you don't have to have a transformer in circuit.

If there's any DC it must be appearing by magic, I think you're confusing resistive loads (power factor=1) with partially inductive ones (PF<1).

 

The genny will be 230V AC, this needs to go into the combo to provide 12V DC to charge the batteries.

 

By far the most likely cause of the buzz is poor quality output from the genny with lots of harmonics in, some combos don't like this and complain by buzzing.

Link to comment
Share on other sites

42 minutes ago, IanD said:

No generator should be more than a percent or two off 50Hz.

 

If there's any DC it must be appearing by magic, I think you're confusing resistive loads (power factor=1) with partially inductive ones (PF<1).

 

The genny will be 230V AC, this needs to go into the combo to provide 12V DC to charge the batteries.

 

By far the most likely cause of the buzz is poor quality output from the genny with lots of harmonics in, some combos don't like this and complain by buzzing.

I never said there was any DC!!!!!!!! And my electrical engineering background makes me well aware about inductive loads and resistive loads.

 

Link to comment
Share on other sites

43 minutes ago, Tracy D'arth said:

I never said there was any DC!!!!!!!! And my electrical engineering background makes me well aware about inductive loads and resistive loads.

 

"The immersion heater is a non inductive load, just resistance. AC current will induce eddy currents and physical stress in inductive loads like transformers, DC does not. "

 

Why mention DC in a comment about the immersion heater being resistive then -- or indeed at all in a discussion about AC mains? And a transformer with a resistive load on the output looks essentially like a resistive load at the input, not inductive -- unless it's a *very* poor transformer with massive leakage inductance, which few mains ones are. Eddy currents and physical stress are nothing to do with the PF of the load, just the current (VA).

 

All this taken together with "Also your transformer will have bee designed to operate in a certain frequency band, likely 50 Hz to 60Hz and the generator may well be producing current outside this range." doesn't suggest an electrical engineering background -- maybe it's the way you tell 'em? ?

Edited by IanD
Link to comment
Share on other sites

1 minute ago, IanD said:

"The immersion heater is a non inductive load, just resistance. AC current will induce eddy currents and physical stress in inductive loads like transformers, DC does not. "

 

Why mention DC in a comment about the immersion heater being resistive then -- or indeed at all in a discussion about AC mains?

 

And you have to admit that "Also your transformer will have bee designed to operate in a certain frequency band, likely 50 Hz to 60Hz and the generator may well be producing current outside this range." doesn't suggest an electrical engineering background... ?

Pardon?   You don't know anything about transformer design Sir, from that comment. Try my experience as IEE trained.

Link to comment
Share on other sites

The generator supply, 230Volts single phase, may be square wave or a true sinewave, if it is a 'true sinewave', this should be ok.

The charger will be making a supply from the generator 230 Volt output by switching transistors, these feed into a transformer coil to make the low Voltage DC; this could be making the laminations in the isolation transformer 'rattle'.

Is the noise there when connected to a shore supply?

If there is no noise from a shore supply, I guess it is the generator causing the problem. The isolation transformer will clean up a poor generator output to a point, but a PC supply may not work too well with a rough supply.

Link to comment
Share on other sites

6 minutes ago, Tracy D'arth said:

Pardon?   You don't know anything about transformer design Sir, from that comment. Try my experience as IEE trained.

I suppose playing the "my electrical engineering degree is bigger than yours" willy-waving game isn't appropriate then?

 

Yes if there's any DC in the system it can cause early saturation of a transformer, but there's very unlikely to be any here coming from a generator -- though it's not impossible. If that's what you meant, you didn't put it very clearly.

 

Incidentally I've actually designed transformers for SMPS in the past, which have all the same issues as mains ones except the frequencies are a lot higher and they melt down much faster if things go wrong ?

 

Edited by IanD
Link to comment
Share on other sites

Your ignorance is showing sir. Just let it go, my experience and training though a long time ago is beyond reproach. Do you remember Ferranti's? We built transformers for the national grid systems in 18 countries. Core and winding design is pertinent to the AC frequency range expected in operation. Been there, knitted the tee shirt and printed it too.

 

My reference to DC was to explain to the OP that AC will make a hum whilst DC with which he is maybe more familiar will not. I never said that there would be any DC component in the generator output .

 

Do not wave qualifications at me even in jest, I spent 45 years in the industry eventually rising to a fellowship.

 

No further posts of yours will be responded to so don't waste my time arguing.

  • Greenie 1
Link to comment
Share on other sites

The printer will have a switch mode power supply containing capacitors and inductors which will have a tuned frequency, This will have an harmonic which is in resonance with the inductive windings in the IT..............At an inspired guess.

Link to comment
Share on other sites

12 minutes ago, Phoenix_V said:

My IT always hums noticeably when I use the (small) laser printer any thoughts on why that is?

I am scanning this to decide if it's a play on words using IT.

 

If not it's possibly harmonics generated by the printer.

 

Link to comment
Share on other sites

2 hours ago, Tracy D&#x27;arth said:

The printer will have a switch mode power supply containing capacitors and inductors which will have a tuned frequency, This will have an harmonic which is in resonance with the inductive windings in the IT..............At an inspired guess.

 

Switch mode power supplies use transistors to switch the supply on and off at high frequencies thus eliminating the need for inductors.

 

This creates the harmonics which Loddon mentions below and it is the harmonics that cause the humming.

 

2 hours ago, Loddon said:

I am scanning this to decide if it's a play on words using IT.

 

If not it's possibly harmonics generated by the printer.

 

 

Link to comment
Share on other sites

3 minutes ago, cuthound said:

 

Switch mode power supplies use transistors to switch the supply on and off at high frequencies thus eliminating the need for inductors.

 

This creates the harmonics which Loddon mentions below and it is the harmonics that cause the humming.

 

 

Them be mosfets then? Arr more 3 legged fuses.

Link to comment
Share on other sites

16 minutes ago, cuthound said:

 

Switch mode power supplies use transistors to switch the supply on and off at high frequencies thus eliminating the need for inductors.

 

This creates the harmonics which Loddon mentions below and it is the harmonics that cause the humming.

 

 

Thats interesting though I have lots of stuff with power supplies which nowadays must all be switch mode and its only the printer that does it ( i had slightly worried that maybe the heating element which I presume such printers have was causing a heavy loading somehow)

Edited by Phoenix_V
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.