pgrange

Featured Posts

Hello everyone 

 

I have a webasto top c heater connected to a calorifier, towel rail and 2 radiators  I ran the heater whilst connected to WTT. I ran only 1 rad upto 50 deg then opened the 2nd rad. Immediately the temp drops to 40 deg then after some time the temperature climbed and topped out at 47 deg. Opening the towel rail the temp dropped again and when the calorifier was opened the temp dropped to 35 deg and couldn't climb any further.  The rads have been balanced.  It's a 57ft boat so I'm wondering do I require an additional pump to increase the flow although there seems to many people running on similar boats with similar loads no problem at all. I'm only running the bedroom rad and towel rail which gets warm but it would be handy to heat the hot water at the same time. Any help would be greatly appreciated. 

 

Many thanks 

 

 

Peter 

Link to comment
Share on other sites

⁹Where are you measuring the temperatures?

What are the inlet and outlet temperatures at the heater after at least an hour with everything on?

What are the inlet and outlet temperatures at the cauliflower?

What size are the rads?

N

Link to comment
Share on other sites

1 minute ago, system 4-50 said:

When you've solved your problem I'd like to know more about your use of WTT.

I think the world is your turtle - That White Trailer Trash - is nowhere safe ?

 

WTT Want To Trade
WTT    Waiting to Try
WTT Watch the Throne
WTT Wild Trout Trust (UK and Ireland)
WTT World Team Tennis
WTT Working Timetable (UK railways)
WTT Well to Tank
WTT Welcome to Tokyo (Tokyo, Japan)
WTT Wheels through Time (museum; North Carolina)
WTT What to Think
WTT Wind Tunnel Test (various companies)
WTT Well-To-Tank
WTT World Turtle Trust (Kailua, HI)
WTT White Trailer Trash (gaming clan)
WTT Windows Test Technology (Microsoft Corp.)
WTT Weapon Tactics Trainer
WTT Warrior Training Task
WTT Web Technology Training (Alcan Aluminum Corporation)
WTT What the Turban
WTT Wyoming Travel & Tourism
Link to comment
Share on other sites

1 hour ago, Ex Brummie said:

What is the output of your Webasto, and what is the combined heating/ hot water load?

 

Thanks for replying. 

 

It's a 5kw heater. As for load everything on the boat was existing other than the towel rail which is 400w. Looking at the size of the rads I'd say 1kw based on similar design / size plus the calorifier 1.5kw? Rough estimate 3.5 to 4kw.

 

Thanks 

1 hour ago, BEngo said:

⁹Where are you measuring the temperatures?

What are the inlet and outlet temperatures at the heater after at least an hour with everything on?

What are the inlet and outlet temperatures at the cauliflower?

What size are the rads?

N

I'm just relying on the temperature as stated in Wtt. 

 

Thanks 

Link to comment
Share on other sites

1 hour ago, system 4-50 said:

When you've solved your problem I'd like to know more about your use of WTT.

Hi 

 

I got it just to see what it does. Its really monitoring software that can also log fault codes. Is there anything specific you'd like to know?I may be able help. 

 

Thanks 

Link to comment
Share on other sites

12 minutes ago, pgrange said:

Thanks for replying. 

 

It's a 5kw heater. As for load everything on the boat was existing other than the towel rail which is 400w. Looking at the size of the rads I'd say 1kw based on similar design / size plus the calorifier 1.5kw? Rough estimate 3.5 to 4kw.

 

Thanks 

I'm just relying on the temperature as stated in Wtt. 

 

Thanks 

For those of us who have no idea what you are talking about WTF is WTT ?

Link to comment
Share on other sites

I don't think increasing the flow rate will do much, unless the Webasto is turning itself down because it has got up to running temperature.  Is it?

The temperature drop when opening up another device is to be expected, as you are adding cold water to the circulating system. The flow temperatures seem low, (especially the 35 degrees, which isn't even lukewarm.) although I've never measured ours. Our Webasto runs for an hour at a time, and is usually still on full output when shut down. It runs calorifier heating, and two radiators. More info required, I think, as per BEngo's post.

Link to comment
Share on other sites

2 hours ago, pgrange said:

Hi 

 

I got it just to see what it does. Its really monitoring software that can also log fault codes. Is there anything specific you'd like to know?I may be able help. 

 

Thanks 

Does it need a hardware componenent and if so, is it expensive?

Link to comment
Share on other sites

11 hours ago, system 4-50 said:

Does it need a hardware componenent and if so, is it expensive?

Yes it requires a USB dongle. The lead itself is comprised of 3 wires. 12v +ve and - ve supply plus a signal wire which connects in my case to the webasto wiring harness. I got mine on ebay for about £45 for both the dongle and a copy of the WTT software. 

 

Peter 

  • Happy 1
Link to comment
Share on other sites

11 hours ago, Iain_S said:

I don't think increasing the flow rate will do much, unless the Webasto is turning itself down because it has got up to running temperature.  Is it?

The temperature drop when opening up another device is to be expected, as you are adding cold water to the circulating system. The flow temperatures seem low, (especially the 35 degrees, which isn't even lukewarm.) although I've never measured ours. Our Webasto runs for an hour at a time, and is usually still on full output when shut down. It runs calorifier heating, and two radiators. More info required, I think, as per BEngo's post.

As I say I have about 4kw of load. I don't have any means of measuring the temp other than what WTT reports but I know just by touch alone its not very warm when all appliances are working.  

 

This morning I set the timer for 2.5 hours. WTT reports the heater running at "full combustion load" for just over an hour. It then goes into a shut down and cooling cycle before ramping up again even though the temp doesn't reach anywhere near its max. After the initial shut down the heater ramps up again with WTT reporting PL to FL which I read as Partial Load to Full Load.  This will then run at full load until the 2.5 hours are up and then shuts down and cools off.  

 

Any ideas? 

 

Thanks 

 

Peter 

Link to comment
Share on other sites

It sounds to me like, though you may think you have balanced the radiators, you haven't got the flow right. The symptoms sound to me like there's not enough flow in the radiators, so they don't dump enough heat and the return getting back to the Webasto is hot.  This will cause it to go to low output. Open all the radiators fully up and see how you get on. You should find a throttle valve in the calorifier circuit: as a rough set up adjust this (from cold) until the return is noticeably cooler than the feed, but not greatly so or cold. The exact instructions for this balance ought to be in the manual for fine tuning once you've got the thing up and running. 

 

Even once fully set up, your load isn't large for the size of heater - these like to be run hard or they start short cycling which will let them coke up.  I tend to run mine in bursts of an hour, listening for short cycling. Many run them  like home central heating, but they don't really like it.  

 

Of course, you may have another problem, but the above is worth a try before you go fixing a serviceable Webasto for want of a decent load.  Good luck!  :)

 

Link to comment
Share on other sites

2 hours ago, Sea Dog said:

It sounds to me like, though you may think you have balanced the radiators, you haven't got the flow right. The symptoms sound to me like there's not enough flow in the radiators, so they don't dump enough heat and the return getting back to the Webasto is hot.  This will cause it to go to low output. Open all the radiators fully up and see how you get on. You should find a throttle valve in the calorifier circuit: as a rough set up adjust this (from cold) until the return is noticeably cooler than the feed, but not greatly so or cold. The exact instructions for this balance ought to be in the manual for fine tuning once you've got the thing up and running. 

 

Even once fully set up, your load isn't large for the size of heater - these like to be run hard or they start short cycling which will let them coke up.  I tend to run mine in bursts of an hour, listening for short cycling. Many run them  like home central heating, but they don't really like it.  

 

Of course, you may have another problem, but the above is worth a try before you go fixing a serviceable Webasto for want of a decent load.  Good luck!  :)

 

Thanks sea dog. 

 

The flow to the radiators are open fully including the calorifier. I have the returns set from quarter to half a turn. Are you suggesting to open the return valves fully? 

 

Peter 

Link to comment
Share on other sites

58 minutes ago, pgrange said:

Thanks sea dog. 

 

The flow to the radiators are open fully including the calorifier. I have the returns set from quarter to half a turn. Are you suggesting to open the return valves fully? 

 

Peter 

Yup, at least temporarily to see how the Webasto runs with a full flow.  Restrict the calorifier a bit as (perhaps a bit counter intuitively) the hot flow needs to pass through a bit slower to dump heat into the tank and return to the heater at a lower temperature. Otherwise, with it fully open, it'll allow very hot water to pass through too quickly and return causing the Webasto to cycle.  The rads ought to dump enough heat for it not to be a problem there.

Link to comment
Share on other sites

1 hour ago, Sea Dog said:

Yup, at least temporarily to see how the Webasto runs with a full flow.  Restrict the calorifier a bit as (perhaps a bit counter intuitively) the hot flow needs to pass through a bit slower to dump heat into the tank and return to the heater at a lower temperature. Otherwise, with it fully open, it'll allow very hot water to pass through too quickly and return causing the Webasto to cycle.  The rads ought to dump enough heat for it not to be a problem there.

Thanks for that. I'll try that when I get back tonight ?

Link to comment
Share on other sites

5 hours ago, pgrange said:

This morning I set the timer for 2.5 hours. WTT reports the heater running at "full combustion load" for just over an hour. It then goes into a shut down and cooling cycle before ramping up again even though the temp doesn't reach anywhere near its max

I don't have a timer but I see the full load for just over an hour and then the shut down on my newly commissioned thermotop C so I have a similar problem.  It is amazing there is so little info (that I can find) on the net and from the manufacturer.  I will get WTT when I have fully recovered frrom my current Norovirus (excuse me, I have to go some place...).

Link to comment
Share on other sites

44 minutes ago, system 4-50 said:

I don't have a timer but I see the full load for just over an hour and then the shut down on my newly commissioned thermotop C so I have a similar problem.  It is amazing there is so little info (that I can find) on the net and from the manufacturer.  I will get WTT when I have fully recovered frrom my current Norovirus (excuse me, I have to go some place...).

Yes I've trawled all sorts of forums looking for info. An dark art indeed. I do know from trawling the net that some thermo top c heaters specifically the units originally designed for auto applications do shut down after an hour. My particular unit originally came from a Renault truck but with a timer it'll keep on running for longer than an hour. 

Link to comment
Share on other sites

It should ramp up to 82 degrees then cycle down to around 74, it sounds like the ECU is faulty and thinks the water temp is higher than it actually is.

Hope this helps, let me know, I have a good second hand one if you need it.

Link to comment
Share on other sites

33 minutes ago, mick55 said:

It should ramp up to 82 degrees then cycle down to around 74, it sounds like the ECU is faulty and thinks the water temp is higher than it actually is.

Hope this helps, let me know, I have a good second hand one if you need it.

I am dubious about the ECU being faulty.  This type of problem seems to occur more often than would be likely due to faulty ECUs.  But I am no expert.

Link to comment
Share on other sites

I am guessing that the temperature monitoring uses a thermistor and between ECU or thermistor I would suspect the thermistor first, if indeed a thermistor is used. If so is there any chance of you measuring its resistance across a range of temperatures and then comparing it with Webadto data ------------ if you can find it.

Link to comment
Share on other sites

1 hour ago, mick55 said:

It should ramp up to 82 degrees then cycle down to around 74, it sounds like the ECU is faulty and thinks the water temp is higher than it actually is.

Hope this helps, let me know, I have a good second hand one if you need it.

The heater has just been repaired and a new ecu fitted. 

28 minutes ago, Tony Brooks said:

I am guessing that the temperature monitoring uses a thermistor and between ECU or thermistor I would suspect the thermistor first, if indeed a thermistor is used. If so is there any chance of you measuring its resistance across a range of temperatures and then comparing it with Webadto data ------------ if you can find it.

If I only put 1 rad on the temperature will ramp up well last 50 degrees. I haven't run it too as I've been testing it but I think the temp reading the heater is reporting is accurate 

Link to comment
Share on other sites

You say it ramps up well past 50, what water temperature is the WTT actually showing on the graph? after an hour it should be showing 84 at full load before going down to part load, even if the flow is not good, at least some part of the system should be getting hot enough that you cannot keep your hand on it, the whole of the system cannot run lukewarm after an hour of full load, it is just not possible on a small system such as yours.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.