Bubble tester, confused?


Dave W

Featured Posts

I have an ALDE bubble tester fitted in my boat, the instructions to test for gas leaks involves lighting a burner on the hob then depressing the button on the tester for ten seconds or more to look for a bubble which shows gas flowing then retest again with the hob off for about sixty seconds.

The thing is I don’t get the initial bubble, depressing the button instantly shuts the hob off, I guess the flame failure system comes into play. 
Anyone got any ideas? Pretty sure there’s fluid in the bowl but difficult to see.

Link to comment
Share on other sites

2 minutes ago, Tony Brooks said:

Don't bubble testers have a bubble chamber bypass that is normally open and when you press the  button the bypass is closed. If so I suspect the porting into or out of the bubble chamber is blocked.

 

My next question was going to be how the OP knows his bubble tester isn't faulty.

Link to comment
Share on other sites

I notice that under instructon 2C that "leaking bubbles may appear" if there is any leakage.

 

I wouldn't want a smoke alarm that "may" go off in the event of fire, although it would of course be daft to rely solely on such an alarm.

I wouldn't want a carbon monoxide alarm that "may" go off when CO was present, although it would of course be daft to rely solely on such an alarm.

 

So I ask: what is the point of a bubble tester if it is known to be quite likely to fail? Perhaps that is why it isn't a BSS requirement?

Link to comment
Share on other sites

2 minutes ago, Machpoint005 said:

So I ask: what is the point of a bubble tester if it is known to be quite likely to fail? Perhaps that is why it isn't a BSS requirement?

I suppose that 'liveaboards' must be 'disposable' as the BSS requirement for non-qualified Gas examiners is that a Bubble tester MUST be fitted.

 

That suggests that the least qualified examiners are relying on test equipment that "may" (or may not) work, on a population that is in the highest risk bracket (spending most time on the boat)

 

Sounds about right !

Link to comment
Share on other sites

24 minutes ago, Machpoint005 said:

I notice that under instructon 2C that "leaking bubbles may appear" if there is any leakage.

 

I wouldn't want a smoke alarm that "may" go off in the event of fire, although it would of course be daft to rely solely on such an alarm.

I wouldn't want a carbon monoxide alarm that "may" go off when CO was present, although it would of course be daft to rely solely on such an alarm.

 

So I ask: what is the point of a bubble tester if it is known to be quite likely to fail? Perhaps that is why it isn't a BSS requirement?

The full quote is “leaking bubbles may immediately appear“ meaning if it is a big leak it will be immediate, but if a small leak you will have to wait.  So taking out that word changes the meaning, though it could be better worded.

Link to comment
Share on other sites

53 minutes ago, Dave W said:

All I can think is the bubble tester is blocked and actually shuts the gas supply down when depressed?

Sounds right to me, which is why the BSS requires you to first test the bubble tester.  I must admit that about once a month I press my bubble test button to check for leaks, but never do the ‘flow’ test first.  I think I will in future.

  • Greenie 1
Link to comment
Share on other sites

2 hours ago, ditchcrawler said:

There have been several posts on CWF over the years what professionals think of bubble testers

 

Possibly part of that opinion comes from the fact that a bubble tester means no drop test and less work for the professional. So I don't think they are completely unbiased.

 

How many bubble testers are fitted and how many problems are reported? Conversely has anyone ever had a problem with a gas registered professional that didn't do a good job? 

Edited by blackrose
  • Greenie 1
Link to comment
Share on other sites

Well I’ve taken it off, removed the fluid bowl depressed the valve and blown air through it. Reassembled and now it’s working fine. Lovely line of bubbles when tested with the hob on and the ring stayed lit.

I think the initial test is just as important as the leak detecting test. My bubble tester obviously wasn’t working and it’s not even four years old but is due a certificate soon ?

Edited by Dave W
Additional info
  • Greenie 2
Link to comment
Share on other sites

7 minutes ago, David Mack said:

Is a low pressure hose between a fixed regulator and fixed bubble tester compliant with the BSS

As long as it’s <1m in length and complies with the relevant BS EN regs then I believe so, yes. 


Reg 7.9.4

Link to comment
Share on other sites

1 hour ago, Dave W said:

Well I’ve taken it off, removed the fluid bowl depressed the valve and blown air through it. Reassembled and now it’s working fine. Lovely line of bubbles when tested with the hob on and the ring stayed lit.

I think the initial test is just as important as the leak detecting test. My bubble tester obviously wasn’t working and it’s not even four years old but is due a certificate soon ?

 

Glad you managed to fix it and solve the problem. That's informative for the rest of us. Did you refill the bowl with new fluid or was there enough left in there after you took it off?

  • Greenie 1
Link to comment
Share on other sites

There was enough left but I’m ordering some more tomorrow as it’s getting close to the minimum level.

I must admit to being pretty lazy regarding testing. I think from now on I will set a time every month to test gas and my smoke alarms. Maybe keep a log.

  • Greenie 1
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.